Hi,

I'm looking for some advice on LEDs that glow when switched off in a multi-switch circuit.

Last month I replaced our old CFL lamps with multiple LED G9 'chandeliers'. The living room has a dimmer switch and the 20-odd LEDs all work fine.

However the hallway has 3 ceiling fixtures, with about 20 G9 LEDs, and 3 switches - one upstairs and 2 downstairs. They have the same LEDs as the living room but they won't stop glowing -when they are switched off they are almost as bright as when switched on.

Switching the RCD off switches the LEDs off.

My googling leads me to believe that the 40V I can see between live/neutral on the ceiling fixture, when off, is inductive voltage/capacitive coupling. I did buy a "0.1uF + 100 Ohm 250VAC triac snubber" from ebay but it didn't seem to have any effect, and the only other capacitor/resistor I found on my browsing linked to a maplin product.

I had one halogen G9 lying around which I put in the place of a single LED and it, too, glowed weakly as the LEDs shone brightly.

And that's how I've left it for a month but as June 21st has come and gone I need to sort this out. I have learned about as much as I can and am still no closer to a recognised solution.

What can I do to pin this down?

Thanks,
 
This is a bit of a pain in the a**e to be honest. I've looked into this as I've had similar issues.

I did find one solution. And that was to try a different led make.

I replaced nine 2.5watt gu9 bulbs with another nine 2.5watt gu9 bulbs of a different make. The glow no longer occurred. I don't know why.
 
I have found that putting a C/R network (aka 'snubber') across the problem lamp(s) can be effective. You may get away with just one, or you may need more than one.

I used to get mine from MAPLIN (RIP).

RS Components would be a good source or (if you are prepared to risk it) eBay
 
As an eBay Associate we earn from qualifying purchases.
Believe it or not the replacement was one of the cheaper makes.

Crompton.

I had just removed them from another property and replaced them with yet another make because they where breaking at a rate of one per month.

So it gets rid of inductive lighting, but has poor longevity.
Not ideal.

As a result of these issues I no longer supply g9 LED bulbs, I give the customer the task of sourcing and buying them. No come back on me.
 
Hi,

I'm looking for some advice on LEDs that glow when switched off in a multi-switch circuit.

Last month I replaced our old CFL lamps with multiple LED G9 'chandeliers'. The living room has a dimmer switch and the 20-odd LEDs all work fine.

However the hallway has 3 ceiling fixtures, with about 20 G9 LEDs, and 3 switches - one upstairs and 2 downstairs. They have the same LEDs as the living room but they won't stop glowing -when they are switched off they are almost as bright as when switched on.

Switching the RCD off switches the LEDs off.

My googling leads me to believe that the 40V I can see between live/neutral on the ceiling fixture, when off, is inductive voltage/capacitive coupling. I did buy a "0.1uF + 100 Ohm 250VAC triac snubber" from ebay but it didn't seem to have any effect, and the only other capacitor/resistor I found on my browsing linked to a maplin product.

I had one halogen G9 lying around which I put in the place of a single LED and it, too, glowed weakly as the LEDs shone brightly.

And that's how I've left it for a month but as June 21st has come and gone I need to sort this out. I have learned about as much as I can and am still no closer to a recognised solution.

What can I do to pin this down?

Thanks,
Have you measured the current to the fitting with the lamps switched off?
 
Thanks Pete - I'll google them and 'fancy' brands to see if I can find a common factor.

Taylor - I wish I had bought the lights a month earlier when there was a local Maplins! In terms of RSC I find the choice a little overwhelming since I'm not sure if the snubber resistance/capacitance is a standard value or related to measurements on the circuit. I thought the ebay one I got would at least show some improvement even if the values were wrong:
0.1uF + 100 Ohm 250V 250VAC RC network contact suppressor triac snubber Qty1 | eBay - https://www.ebay.co.uk/itm/123075894023
 
As an eBay Associate we earn from qualifying purchases.
Maybe the circuit polarity is incorrect? If the L remains connected to the LEDs there may just be enough capacitive coupling to get a glow. It's just a thought. But can you confirm L is not present at the light fitting when it's off? Any test gear?
 
Maybe the circuit polarity is incorrect? If the L remains connected to the LEDs there may just be enough capacitive coupling to get a glow. It's just a thought. But can you confirm L is not present at the light fitting when it's off? Any test gear?

I just have a DMM and a Maplin analog meter. I guess I'm also working on the assumption that the previous CFLs worked fine with the same circuit (and, possibly noteworthy) when I replaced just the first CFL the LEDs all flashed as (I presume) one CFL took the voltage until it triggered and all the LEDs flashed momentarily and the cycle started again.
With them all replaced I'm getting a glow from the halogen but the LEDs are too-bright to be called 'glowing' - they look 'on' (tbh they are too bright when really on so I may end up replacing them one day anyway).
I'm fairly certain I have to assume it's inductive/capacitive unless there's a simple test I can do to eliminate that (and the simplest seems to be to insert a better snubber in the circuit).
 

Reply to Advice on LED inductive voltage preventing LEDs switching off in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
159
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
525
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
474

Similar threads

Similar queries here previously, eg: Advice (please) regarding suppressor / "snubber" for LED lighting | on ElectriciansForums -...
Replies
1
Views
171
Thank you all for your replies and suggestions. I will try to follow up on each one and find a suitable solution. many thanks all
Replies
4
Views
404

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top