Advice on new kitchen fit | on ElectriciansForums

Discuss Advice on new kitchen fit in the UK Electrical Forum area at ElectriciansForums.net

W

WOMick

Hi

I am new to the forum and would like some expert advice on my kitchen planning and also a sanity check on the maths please.

I will be replacing a kitchen into a 20 year old house, so fairly modern build. The built in gas oven/grill is currently housed in a tall cabinet with a gas hob on an adjacent wall. The intentions are to replace with a built in single electric oven with built in microwave above it. The gas hob is to be replaced with an induction hob. A gas safe engineer will be capping the supply to the old gas oven and gas hob.

All appliance socket outlets (fridge, dishwasher etc) have FCU's fitted above the worktops with 2.5mm T&E so a good starting point. There is also a socket outlet on the wall behind the built in oven with an FCU adjacent. A 32A cooker supply has also been installed with 6mm T&E (at build) near to the gas hob but which has remained redundant due to no stand alone electric oven / hob (gas hob currently fitted).

So, my plan.......firstly installing the single electric oven and microwave:
Single Oven is rated at 2.9kW total load
Microwave rated at 900W
Fit the oven with 2.5mm heat resistant flexible then into a plug and utilise the existing socket outlet at rear of the original tall cabinet (this is protected by 2.5mm T&E 13A FCU). With a 12.6A draw from the 2.9kW oven and then applying OSG diversity regs it will be 10.78A (10 + (2.6 x 0.3)) so seems absolutely fine. I would then run an additional 13A FCU in 2.5mm T&E for the microwave above with socket outlet for the microwave.
Knowing that the there are mixed feelings regarding using plugs for built in single ovens (this one isn't supplied with cable or plug) I wanted some advice firstly as to whether this installation is safe but also whether my maths are correct and the install is permissable / notifiable. Considering the oven has been deliberately chosen as <3kW is it therefore acceptable to use 2.5mm flex + plug + existing 13A FCU / socket outlet?

Second plan is for the induction hob.
Rated at 7.4kW
I intend to utilise the existing 32A radial and wire straight into the CCU with 6mm butyl. The existing cooker isolator also has a socket outlet so I have added the 5A to the diversity equation. Can't see a problem with this at all but would appreciate a more experience person to give it the thumbs up. (7.4kW = 32.174A therefore with diversity regs = 21.65A (10 + (22.174 x 0.3) + 5).

So that's about it apart from the big money question.....is any of the work notifiable? Any advice or guidance will be most appreciated.

Mike
 
sounds a decent plan. i would put the oven on a FCU rather than a socket, or better still,install a 2.5mm dedicated radial 0n a 20A MCB. it's quite a heavy load for the rFC when you consider other allpliances as well.
 
Thanks for all the comments guys....most appreciated. How does the maths look in my original thread? Like the idea of a separate radial(thanks telectrix) but I'm trying to keep away from having to run a separate radial to the consumer unit and therefore if the facility exists (in line with the regs and safe) to utilise the socket outlet and 2.5mm heat resistant into a plug for the single oven then I would rather go with that. Problem is, am i allowed to? I think the regs state that any fixed installation >2kW needs to be hard wired if I remember rightly?

What are your thoughts on the induction hob? Sound ok?
 
As I suspected, the 'jury is out' on fitting the single oven lol. Has anyone fitted a single oven rated at <3kW with 2.5mm heat resistant flex + plug into a socket fed from a 13A FCU? If so and it is permissible in line with the regs, it will make my kitchen install a whole lot easier. I presume no one has any issues with the induction hob on the 32A radial?
 
As I suspected, the 'jury is out' on fitting the single oven lol. Has anyone fitted a single oven rated at <3kW with 2.5mm heat resistant flex + plug into a socket fed from a 13A FCU? If so and it is permissible in line with the regs, it will make my kitchen install a whole lot easier. I presume no one has any issues with the induction hob on the 32A radial?

I think you'll find that most <3KW single ovens come with factory fitted cord and 13A plug top these day's!! lol!!
 

Reply to Advice on new kitchen fit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I've put a 2 way unit inside kitchen cupboards before now if we were re-using the original cooker supply but the customer wanted 2 x 16A ovens. I...
Replies
8
Views
440
  • Question
There is no reason for an item of fixed equipment to be on its own dedicated circuit just because it is fixed equipment. There may be other...
Replies
2
Views
490
loz2754
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top