Hi all,

Ive just come back from looking at a job. Customer has 3 electric heaters in thier flat only one is working. Had a look and the one that works seems to be wired into the ring main. The 3 15a radials wired in for the heaters have no power getting to them. The board is a split feed with no RCDs one side works fine but the side that has the 3 heaters on has no power. If I disconnect everthing and straighten out the feeds so I get power am I required to RCD them as well? There is a 40a add on to the side of the CU for the shower which has no rcd either. If I get involved in this am I going to be responsible for everything else?

All advice as usual gratefully received! :confused:
 
No definatly not eco 7. My mistake! the side that has sockets and lights on is rcd protected the side that has no protection only has the 3 radials for the heaters on. Apologies!
 
My take on things is that if you are modifying the circuit you will have to RCD it/them.

Thing is though, as the side of the CU that doesn't have RCD protection, its normally fed right out of the main switch, along with the link that feeds the RCD too, so can't see how you don't have any voltage there?
 
Someone has definatly been messing with the feeds. There are the main incomers then a feed onto the split side and a feed for the shower cu shoved in and anther which I havent traced yet. It looks like the feeds have been split which is why no power on one side if that makes any sence ( should have taken a picture! ). I just want to know if the heaters will need rcd protection once the feed mess is sorted. There in bedrooms run behind platerboard. In the riser in the hall there are 3 lives in 16mm in a small henly and neutrals go straight in through wall!
 
What can I say it's a mess! Think I will go in on an hourly rate and just try and get it all safe and 17th! Thanks for your time people it is appreciated especialy as my discriptions are as clear as mud!
 
Sounds very much like you have 24 hour supply to one side and a night time taffif on the other side, Is there a single point of isolation for this board?

Sounds like you will have to fit another board and move the storage heater into it to comply with the regs.
 
Sounds very much like you have 24 hour supply to one side and a night time taffif on the other side, Is there a single point of isolation for this board?

Sounds like you will have to fit another board and move the storage heater into it to comply with the regs.

It does sound like there are two supplies (dual feed board), but why are you saying he'd need to fit another board and move the storage heater into it to comply with the regs?
 
Double feed board does sound logical but no sign of an accessable timer for heaters. Also one feed is split between the two sides of the board.
 
From the description it dose not sound like it is clear even to an electrician how this board is set up. Currently it presents a danger asit sounds from the op that its not clear how to isolate the storage heaters, from the description it dose not comply with 132.1. one way to make this clear for unskilled persons to be able to isolate circuits safely would be to install a board for the heaters, more information from the op would help to come up with a list of other options tahs may also make it clear what dose what and how to operate it.
 

Reply to the thread, titled "Advice on regs please" which is posted in Australia on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Advice on regs please
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
22
Unsolved
--

Advert

Thread statistics

Created
Shock Doctor,
Last reply from
Spudnik,
Replies
22
Views
1,928

Advert

Back
Top