Hi all, new to posting but been reading for years.

I inherited a house from my grandmother who passed in 2021, I intend to renovate and rent out, step by step, job by job as money allows.

Getting the property ready to rent has uncovered a fair few jobs needed to bring it out of the 1970's

I knew the electrics needed sorting so found an electrician via Check-a-trade website. He inspected wiring and said I just need an upgrade to the consumer unit. old system was 2 old bakalite cu's on day night mode I think it was called (2 different tariffs for day and night)

So he quoted and installed a single consumer unit dual rcds. 5 original circuits but I told him to disregard the shower as I would be installing a mixer tap shower .

Circuits now are, Cooker, Lights up & Lights Down on same breaker, Sockets Up and Sockets Down on separate breakers (He said their all radial circuits)

Now here comes the question as I don't think its safe.

He has installed the new consumer unit half on and half off the wooden board that the meter and main fuse are on.

Used 1 screw to fix it, the half of the consumer unit hanging off the wooden backing board there is a 30 to 35mm gap behind to the wall.

There is one screw in the bottom left into the board (I know, I took the cover off (I did safely isolate)) The CU is so unstable and wobbly.

He has had to move the CU approx 10 inch down and 14 inch to the right, so he has joined the wires above the ceiling to extend them by using junction boxes (Old bakalite types, so they must have already been there) They are free hanging between the joists under the bedroom floorboards which is just above the CU on the kitchen wall.

CU is installed at top of kitchen wall (2200mm from floor level, approx) so not accessible for kids to pull off wall or anything but it is still very loose.

There is no strip around the rear entry knockout and no fire barrier, just a large knockout with the several wires coming in.

Is this right? Safe? I need a EICR before I rent, will this even pass with those issues?

I can take photos and post them if you can't quite get what I mean.

Thanks in advance, I just want to be prepared in what I say when (if i should) call him back in to put it right.

Now, maybe the thing that should have rang alarm bells is he charged ÂŁ250, is that too cheap?, I have had a glance on line and seen its usually ÂŁ400 upwards.

I did as mentioned get him through check-a-trade so thought he would be reputable and everything, ultimately I want to know where I stand before contacting them and him.

thanks for the patience in reading this long winded post.

David
 
It's definitely not a neat install or one done with good workmanship, but I'd say it would be unusual to get that for ÂŁ250.

The board is a Screwfix special, but he did splash out and fit Type A RCDs, so 69.99, instead of the ÂŁ49.99 option. He also used a gland for the meter tails, so he is already some way ahead of the average DIY board changer.

It should definitely be secured more firmly - with battens between it and the wall where it overhangs, and the wires to the top of the MCBs should really be better installed, with no copper on show - but then the BG supplied cables fail on that basis too!

There should also be a plastic cover sitting in front of the bus bars, so that even removing the front cover does not expose lots of live copper...

Other than that I'm not actually seeing anything that would count as unsafe. You mentioned the extended cables, but there's no picture of that so tough to make comment.

Check online with NAPIT if you haven't already that he is actually registered, as it's been known for people to claim membership of a scheme when they aren't.

If he is a NAPIT member, then that will give you some comeback should there be a problem. Check that he will be providing a Part P certificate, as well as an Electrical installation Certificate.

If you get those, then there is probably not much to be concerned about. I would not use him for the EICR though, as that will give you an independent and more thorough inspection that what he has done is at least safe.
 
Thanks to all that have replied, I have checked Napit site, he is on there as Domestic Installer EAS/CPS. I will take more photos under the floorboards just above the CU in the bedroom floorspace where the JBs are, and upload the certificate he gave me.

Apart from that, and pending all of the good folks advice on here regarding the JBs, should I be at least be asking him to come back and secure the CU better by putting some battens under the overhang side?


Regards

Dave
 
So who took the decision on it being a TNC-S supply

Just to add to your question, it may help it may not. I am one of the end terrace of a terrace of 7. We are all on a looped supply, 1 loop comes up my side wall splits to mine then feeds 2 other properties so 3 of the 7 from the incoming loop on my wall, then the remaining 4 in the terrace are looped together on a separate incoming loop on the end of the wall of the other end terrace the other side.

Its a rubber incoming cable with 2 cores. The earthing arrangement has always been like this.


I have also attached a photo of the setup before he came in and installed the new CU
[ElectriciansForums.net] Advice on safety of new Consumer Unit Install


On another note regards the loop, have a look at these pictures and see how dangerous this looks to you

[ElectriciansForums.net] Advice on safety of new Consumer Unit Install
[ElectriciansForums.net] Advice on safety of new Consumer Unit Install
[ElectriciansForums.net] Advice on safety of new Consumer Unit Install
[ElectriciansForums.net] Advice on safety of new Consumer Unit Install
 
Whatever you do, DO NOT put your ladders anywhere near those supply cables.
a call to the dno to inform them of damage to your supply cable would be prudent.
Yeh… I had a bit of a panic when I saw that close up of the incomers.
 
Is that overhead supply? Looks like it was TT and the installer converted it to TN-C-S perhaps without DNO approval. Another point to raise with the DNO, not so much to catch out the guy but to ensure regularisation of conversion as some areas cannot/will not convert. I see the seals have been removed so looks like a bit of a chancer on the job. Exposed copper at the terminals and can't wait to see the JBs' if the terminations in the JB echo the CU well I think it would profit from an inspection and perhaps remedy. I wonder what the test results were??? In any event looking at the supply wire, if indeed they are in use, the "electrician" should not even have started work without getting the DNO in first so that is a bit worrying.
 

Reply to Advice on safety of new Consumer Unit Install in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top