Hi,

I'm looking to get the lionshare of a small shed wired before a friendly electrician does the needful. I'm a confident DIYer, but I would appreciate any more experienced view to check my logic.

My house was professionally rewired in 2022, but I would like to connect a small 8x6ft shed to a secondary CU that's close by. Connecting to the main CU would require too much upheaval.

The shed is small, but I'm planning to install a few sockets for charging power tools and occasional use of garden tools - plus an internal and external light. No big loads.

Obviously, it's a very simple issue, but I'd appreciate a more experienced view on any issue with my connecting to the secondary CU. The 12m SWA run is clipped externally but fiddly with tight access, so keeping that deliberately light also. Just keen to avoid anything daft before my friend sees it!

Many thanks in advance.
Blank diagram.jpeg
 
Am I seeing 3 RCDs in series there 😁
Quite right - seems this was a diagrammatic error upon checking, thank you. On checking the secondary CU does not contain an RCD. I'm now thinking this is overengineered for my purposes and that I'll just put in some SWA, and my friend can hook up a simple radial circuit when he gets time. Much thanks.
 
Quite right - seems this was a diagrammatic error upon checking, thank you. On checking the secondary CU does not contain an RCD. I'm now thinking this is overengineered for my purposes and that I'll just put in some SWA, and my friend can hook up a simple radial circuit when he gets time. Much thanks.

Have you done the calculations on the 2.5mm SWA?
 
what else is on the secondary DB?
How far is the shed from the Secondary DB?
2.5mm2? nope not big enough, in fact allow for the future, get a decent size cable in there, again though what is on the Secondary DB?
 
PVC/SWA cable is quite rare now locally but can get it to order so now we just use xlpe/swa cable as standard.
But my point is a DIYer even a confident DIYer might not know the difference and assume any 2.5 cable is capable of greater than 32A when buried without considering other factors!
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
thedawnbefore,
Last reply from
thedawnbefore,
Replies
25
Views
2,279

Advert

TrueNAS JBOD Storage Server

Back
Top