Skys

-
Joined
Mar 16, 2019
Messages
84
Reaction score
93
Location
Barnsley
When carrying out Ze with main earth disconnect I get a reading of 77.25 ohms. All good. When main earth is reconnected and all parallel paths in place reading comes down to 0.60 ohms. I have 3 lighting circuits not covered by an rcd all Zs readings are well in permitted Zs. Would any body apply a code to this when carrying out a EICR. Never had this scenario that the Zs falls so low on a TT due to parallel paths . Thanks
 
DNO very often won't give PME in this situation due to multiple supplies within a commonly bonded structure.
Quite fortunate in that the landlord of this unit has had it from day 1. He pulled all his paperwork out and seems different sections /rows had different dnos. One side of this section is SSEN who have PME this part is an IDNO. Each phase was different builder's, dno etc... I have done a lot of work in units there. Fitted a few ev chargers...
Treated all the units as pme despite the rods as safest option. Fitted matt:e on earlier installs and then zappis
 

Reply to Advice on TT system in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
717
  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
2K
OLDBOY
O

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top