Buckfast
-
Called to a property today to carry out repairs etc. When completed customer asked me could i have a quick look at photovoltaic system. Received only one cheque in 2 1/2 years for generation. Invertor was not generating.
Invertor is an Eversol TL 1500 giving a fault of, 'Output Relay Fault'. The system has 8 panels mounted on garage roof and these are connected as two strings of four which are then connected in Parrallel at the DC isolation switch with only one +ve -Ve going to invertor. String one gave me 204 Volts and String two gave 196 Volts DC. The input supply to AC isolator ok at 240V. Tried rersetting invertor with same fault appearing. I would say invertor fault ?. But if invertor replaced could i not connect all panels in series ? as long as this was less than the max input DC voltage. Is there a reason why they would be wired in parrallel.
Invertor is an Eversol TL 1500 giving a fault of, 'Output Relay Fault'. The system has 8 panels mounted on garage roof and these are connected as two strings of four which are then connected in Parrallel at the DC isolation switch with only one +ve -Ve going to invertor. String one gave me 204 Volts and String two gave 196 Volts DC. The input supply to AC isolator ok at 240V. Tried rersetting invertor with same fault appearing. I would say invertor fault ?. But if invertor replaced could i not connect all panels in series ? as long as this was less than the max input DC voltage. Is there a reason why they would be wired in parrallel.