Joined
Jul 7, 2018
Messages
6
Reaction score
3
Location
Isle of Man
I have been doing some tests around our property here and I cannot get the earth resistance test to get anywhere lower than 1.86k, even started tested now up to 30 meters away from the property and still cannot get any lower readings.

Any advice would be greatful.

Kind Regards

James
 
Earth Rods are being hit in to their entire length, approx 1m deep, cannot get much deeper as we are hitting bedrook, have tested using |KEW-5105A and then tried removing the earth rood and testing again 1 meter further away from the property and so on, but cannot get the reading to get any lower. The soil is not the best, looks as though its had about 100 years of tiles, bricks and plaster pored into it.

1m is not deep enough to get an Ra which is stable long-term.
And using just one rod is not a very good plan either.
You need to go deeper or else find another method of installing an earth electrode
 
They kind of live in the middle of woodland, on a hill that seems to be basically baserock with a light covering off soil and roots, all looks lovely but a real pain at the moment, I have not tried Tape yet, I was kind of hoping that this would be a simple fix somewhere along the line, Will have to pop to Yesss on Monday to see if they have any tape in stock, Thanks guys for the help, Very much appreciated.
 
Do you have access to another test instrument to make sure your meter/ leads are not faulty.

If the ground is hard you need an sds max gun with an attachment to make easy work of it, I’ve done an install at Loch Lomond where the ground was full of rocks, it can make a lot of difference if you sharpen the end of the first rod to a point as this can break small rocks or help deflect the electrode when going down. As others have said you’ll need more than just one electrode for stability , I usually go for a minimum of 3 1.2 m you may also need multiple electrode sites. The above job I mentioned we hade 5 electrode pits with 4 electrodes deep as the soil resitivity was poor although we were looking to achieve an Ra of under 10 ohms
 
0.74ohms can't be going through the earth surely, did you touch the water supply pipe on the way down and are going back to the network via someone else's bonding?
I didn't install it, only tested it, it's been in the ground 15 years.

I reckon it's hit another service on its way down, according to the paperwork the rod is 5/8" and 3m long so not a twig by any means.
 
Got to page 403 then gave up

Fore warned ..403 Went straight to appendix-es ..
Now getting bored with list .

EARTH ELECTRODE SUBSYSTEMS -- 11, 24, 25, 31, 33, 44, 51, 52, 63, 64, 65, 66, 70, 7 1 , 85, 86, 87, 8 9 , 101,
107, 120, 131, 137, 138, 145, 148, 170, 187, 190, 196, 205, 212, 213.

213 ..FAIL ..mostly surface corrosion /good connection (+ RF Impedance)

.... Then got side tracked with memories "Things wrapped in Brown wax paper ,in heat sealed polythene bags..."
( may see if my -Inner lucky stumble , is working later )
 
Managed to get it down to 112 Ohms, after paying out a small fortune, 3 earth rods later all connected with flat copper tape (25mm x 3mm x 25m) dug into the ground about 12” deep, couldn’t get any deeper due to roots and rock. Thanks guys for the advice
Cool, go back when you've had a couple of days rain and test again, just out of curiosity.

Personally I wouldn't have bothered with rods and gone solely for tape.
 

Reply to Advice Wanted - VERY High Earth Resistance Problem in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
706
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K
  • Question
When I was at college doing the 2361 back in the 1980's I still recall to this day the instructor (Mr Wood) saying "Lads I do not want you to...
Replies
10
Views
520

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top