Hi everyone,

I would really appreciate some advise. I'm a domestic electrician but my neighbors asked me for some help on a issue he has and here I am.

So my neighbor has a tree surgeon company, they have a yard where the cut and dry logs as well. So they've just got a new drying system installed and have a new 20KVA generator to power the yard. A few weeks ago the generator started spewing oil, the manufactures said it's because the generator is be under loaded, so they said they should ideally run the generator at 12KVA to be most efficient.

I went to the yard today and the supply is 3-phase. I measure the current drawn on each phases as L1:4.4amps - L2:0.4amps - L3-1.0amps

Total loading 5.8amps. If I put this into KVA I get 4.0KVA on 230v and 5.8KVA on 400v.

I worked out 12KVA to be around 17.3amps

Any if the above i correct or am I completely wrong somewhere. Also any advise on the best way to increase the loading, the yard is ran 24/7 and is in constant us. I was thinking of a dummy load, but wanted to get other opinions or ideas! I've attached a pic or 2 of the generator and controls.

Any advise is welcome.

[ElectriciansForums.net] Advise needed. Diesel generator loading issues


[ElectriciansForums.net] Advise needed. Diesel generator loading issues
 
Hi,i know the Perkins 404D engines,fitted to these,and if it is "spewing oil",it will not be your customers use...it has other issues.

They are a relatively small,non-turbo engine,and,are not under loaded,as such.but are stretched,at maximum output.

I have seen many identical engines with hideous hours clocked,which do not jetison the black stuff. There are many reasons for the oil expulsion,and this wants diagnosing first.

Blocked breathers,failed gaskets/seals,fractures,wrong oil,worn bores due to air filter issues,running hotter due to radiator clogging and degrading the oil,and a few more besides.

Bore glazing and similar problems occur more frequently in larger engines,with larger,slower swept mass components,such as the bigger Cat engines. An old and far from HS at W approach,was to run these engines up to half max rpm,and drop a glass petri-dish in the open inlet tract....this allegedly got them bores back to cross-hatch ;)

I could show you a very old Gen-set 17 kVa unit,which has been on me pals yard for nearly twenty years,in daily use,minor lighting 99% of the time,occasional hand tools. Similar 4 cyl n/a engine,and that goes through nothing but diesel.
 
I'am no diesel mechanic
but even I know running a 20kva genny
for long periods on a small load like that is problematic
you should consider either solar & batteries for night
And run the BIG genny during the day only.
Or have a smaller say 2kva for night.
 
Do we know if these generator engines are run-in in the factory or is there a strict run-in procedure that has been neglected?

I've seen plenty of well broken in generators run nothing but light loads for years on end and they don't use a drop of oil!

If it's bore glazing I would recommend finding a monograde SAE30 oil and running the engine with high but continuously changing loads for several hours.
 

Reply to Advise needed. Diesel generator loading issues in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top