I am installing an AEG HK654200FB 7.4kW induction hob. It will be on its own 6mm radial circuit supplied by a 32a Type B MCB. After reading the manual for this particular hob it says that it has an extra power function which only lasts for a maximum of 10 minutes on each ring which if all were on this setting would make the total load the following:
Right Rear 2800w 10 mins
Right Front 2500w 4 mins
Left Rear 2800w 10 mins
Left Front 3700 10 mins
Total - 11.8kw
At nominal power (max heat setting)
Right Rear 1800w
Right Front 1400w
Left Rear 1800w
Left Front 2300w
Total - 7.3kw
Now I'm uncertain that my design will be ok, I can't really need 10mm with a 50a MCB?
Also, I think its going to turn up without a connection cable, from the manual I read that I need some H05BB-F Tmax 90°C it doesnt specify size but I would say I need 6mm or 10mm @ 90. H07 is +85 degress but seems to be available at 6mm and 10mm 3 core. Can anyone shed some light whether this power function causes a problem with a standard 6mm 32a design and whether h07 would be suitable?
Thanks
Right Rear 2800w 10 mins
Right Front 2500w 4 mins
Left Rear 2800w 10 mins
Left Front 3700 10 mins
Total - 11.8kw
At nominal power (max heat setting)
Right Rear 1800w
Right Front 1400w
Left Rear 1800w
Left Front 2300w
Total - 7.3kw
Now I'm uncertain that my design will be ok, I can't really need 10mm with a 50a MCB?
Also, I think its going to turn up without a connection cable, from the manual I read that I need some H05BB-F Tmax 90°C it doesnt specify size but I would say I need 6mm or 10mm @ 90. H07 is +85 degress but seems to be available at 6mm and 10mm 3 core. Can anyone shed some light whether this power function causes a problem with a standard 6mm 32a design and whether h07 would be suitable?
Thanks