hey guys
we have done an EICR on a 2 bedroom bungalow, the supply is a 25mm 4 core 3 phase SWA to the property, it is supplied from 80amp fuse.
although it is speculative as the cable is underground we reckon the distance is around 600m :fearscream:.
it has being installed around 10 years and no evidence of thermal damage or any concerns of equipment not functioning correctly as per tenants.
the Zdb is 1.89 so disconnection time is not achieved either. the volt drop is around 72volts based on potential load of 80amps.
there are no 3 phase circuits in the installation but it is fully electric so it does have 6 panel heater and an electric hob/oven.
what code would you give based on the voltage drop allowance not being achieved.
 
Last edited:
hey guys
we have done an EICR on a 2 bedroom bungalow, the supply is a 25mm 4 core 3 phase SWA to the property, it is supplied from 80amp fuse.
although it is speculative as the cable is underground we reckon the distance is around 600m :fearscream:.
it has being installed around 10 years and no evidence of thermal damage or any concerns of equipment not functioning correctly as per tenants.
the Zdb is 1.89 so disconnection time is not achieved either. the volt drop is around 72volts based on potential load of 80amps.
there are no 3 phase circuits in the installation but it is fully electric so it does have 6 panel heater and an electric hob/oven.
what code would you give based on the voltage drop allowance not being achieved.
C2 but for not meeting disconnection times or max ZS.
Even the supply cable a BS88-3 80 amps has a max ZS of 0.4 ohms 80% value
 
The cable is way undersized.
If the voltage drop is detrimental to the installation I would make a mention of it as volt drop generally is not considered for an EICR.
 

Reply to exceeding voltage drop in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
That looks like a Metrel display (I have one), they have a permanent 3 wire display that measures the three combinations so I would say that’s a...
Replies
5
Views
775

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top