So there you shifted from the statement
to "openly prevent parallel arcing" consistency man consistency!
And not to muddy the waters but I feel the need to mention this now before someone asks latter:
UL has a very broad range (blanket) of what they call arcing. Traditionally arcing has revolved around Paschen's Law. However, because continuous arcing is impossible to sustain at 120 volt unless heavy carbonization is present UL had to come up with their own definition of 'a luminous discharge between electrodes...' meaning that even a sputtering short circuit fits their definition of arcing.
They needed to do this because arcing is not a concern at 120 volts the way it is at 230 volts.
However- short circuit or an actual arc- UL testing has shown that MCBs and RCDs can mitigate all parallel events.
................................................
In other words they knew actual arcing is possible at 230 volts nominal.
They and the CMPs for years knew arcing is possible at higher voltages hence why for decades prior 277/480 volt services of 1000amps or greater required and still require a GFP main breaker.
UL knew arcing at 120 volts is typically not possible.
So UL changed the definition (twisted the definition) to say arcing can take place at 120 volts.
And came up with the over driven carbonized path staple theory as a backup should the definition be called out.
UL proves the European system detects arcing at all voltages. UL then says this system needs to be implemented in the US. UL then puts on a show telling the CMP this system needs to be replicated in the US.
But because we are to dumb to be educated on loop impedance and UL pontificates perspective fault current is far lower at the service then it typically is- we must us an electronic breaker instead.
That is an over simplified version of it.
All the while UL, CPSC and CMPs are following the beat of Eaton and other manufacturers.