Evening all,

Just after some info on the photo attached. It’s a tn-s system with an Earth going to the cu met from under the floor boards. After lifting the boards I found the earth attached as so... I was expecting to see a clamp around the supply cable, not a choc block with legs of unknown origin attached. Can anyone enlighten me on what’s going on here? Thanks

[ElectriciansForums.net] After some advise please- Tn-s earth arrangement
 
By way of an example... consider an SWA supply from the meter to a consumer unit some way away. There are various joins in that connection, this is acceptable. I find it hard to believe a correctly made join (say a crimp or a service terminal block) would not comply.
 
Just because people can't be asked to study doesn't mean they can substitute opinion for fact.

I'm not stating an onion - its fact that "continuous" is not in the BYB or BBB

There is NO requirement that I am aware of for any spark to own and read all the Guidance Nuts .............

If this was so important, why isn't it stipulated in black and white in the BYB or BBB? Its not ..........................
 
The purpose of the 'continuous guidance' is to prevent loss of bonding downstream where a single conductor loops from one service to another should it be partially disconnected. There is guidance somewhere, I cant remember where, and that guidance also states that a durable maintenance free joint is acceptable, such as a non insulated crimp ferrule. But none of the above is a requirement of Bs7671
 
Show us the regulation that stipulates earthing and bonding conductors have to be one continuous cable segment.
SC I did say clearly its Not in the Regs but stated in the GN8.
By way of an example... consider an SWA supply from the meter to a consumer unit some way away. There are various joins in that connection, this is acceptable. I find it hard to believe a correctly made join (say a crimp or a service terminal block) would not comply.
A soldered connection or single MET are deemed acceptable
So its not a reg then.

End of.
We all know the Regs are not statutory, but they are the only code of practice we have. Guidance notes are supportive, like the Parts 1 to 7 of the Building Regulations

If you've got access to the NIC's technical manual, it's in part B37-21, section 7.
 
We all know the Regs are not statutory, but they are the only code of practice we have. Guidance notes are supportive, like the Parts 1 to 7 of the Building Regulations

If you've got access to the NIC's technical manual, it's in part B37-21, section 7.

But you are stating them as if they are 100% regulations which they are not ........... so please stop.

Do a survey on how many sparks have the BBB or BYB plus all the guidance notes ................. I suspect it won't be many...........

As for the NIC manuals - no I don't and as they don't write the regs, its not relevant ......... they could be promoted as NICEIC "best practice" but the NICEIC still couldn't pick members up on assessments for things like this................... they can't be arsxd to follow up on poor practice of their members either ........... yet dare to use their logo and not be a member - you'll be up in court ..... misplaced priorities IMHO
 
What Conductor did you think you were following?

If that is the main earthing conductor, then you have a problem and would need to call out the national Grids local sub contractor to your area ( possibly UKPN)to look at fixing a new earthing point to the SWA of the Sub main cable. They will charge for this service.
If they cannot do this, you would need to look at changing the earthing system to a TT system or having the supply cable replaced with a TN-C-S

I would Inform the customer of the bad news, its not something which can be ignored even if you're getting a good Ze reading
 
What Conductor did you think you were following?

If that is the main earthing conductor, then you have a problem and would need to call out the national Grids local sub contractor to your area ( possibly UKPN)to look at fixing a new earthing point to the SWA of the Sub main cable. They will charge for this service.
If they cannot do this, you would need to look at changing the earthing system to a TT system or having the supply cable replaced with a TN-C-S

I would Inform the customer of the bad news, its not something which can be ignored even if you're getting a good Ze reading
It’s the ONLY “earth” cable going to the cu. There was no earth clamp at the top of the supply cable so I thought maybe for some reason the connection was under the floor board as that is where the “main earth” was coming from to then enter the cu. Upon lifting the board that is what I found! Pulled on the bare cables and they didn’t budge, all head off slightly different angles!!
 

Reply to After some advise please- Tn-s earth arrangement in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
391
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
975
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
A bit like saying plumbers makes good electricians. 🥴
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top