Ive search the forums and cannot find a conclusive answer.
I have been reading my New Regs Book today (Thank you sam400) and the IET BSI changes within BS7671:2018.
Now it says 'chapter 42 protection against thermal effects:- New regulation 421.1.7 recommending installation of arc fault devices. now when you read this regulation is says as above. The AFDD shall be placed at the origin of the circuit to be protected. Example: Premises with sleeping accommodation.
Now that to me would be a domestic dwelling, yet when i ring wholesalers i just get the reply 'Nobodys fitting them! We have no call for them! or Waiting to hear back from supplier!'
Now when it comes to SPD devices they are being pre fitted into consumer units now, even with type A RCDs.(Hager)
Id like to install Schneider but they dont seem to do anything 18th yet.
My Question is Regs say they need to be fitted. Can you get a main one to cover all or should i just fit them to the lighting and sockets where the bedrooms are? or every circuit?
Not fitted any AFDD's myself yet so what do you guys do and what manufacturers do you use?
I have been reading my New Regs Book today (Thank you sam400) and the IET BSI changes within BS7671:2018.
Now it says 'chapter 42 protection against thermal effects:- New regulation 421.1.7 recommending installation of arc fault devices. now when you read this regulation is says as above. The AFDD shall be placed at the origin of the circuit to be protected. Example: Premises with sleeping accommodation.
Now that to me would be a domestic dwelling, yet when i ring wholesalers i just get the reply 'Nobodys fitting them! We have no call for them! or Waiting to hear back from supplier!'
Now when it comes to SPD devices they are being pre fitted into consumer units now, even with type A RCDs.(Hager)
Id like to install Schneider but they dont seem to do anything 18th yet.
My Question is Regs say they need to be fitted. Can you get a main one to cover all or should i just fit them to the lighting and sockets where the bedrooms are? or every circuit?
Not fitted any AFDD's myself yet so what do you guys do and what manufacturers do you use?