I would like the gather some alternative views on earthing systems and which one would be correct for agricultural premises.

It is to my current understanding that where livestock are present an earth stake should be used.

Can TN-C-S be extended from the distribution board to another consumer unit, and then onto another one again?

Also, when is it ok to use SWA sheaving as a main earth, and when is it not?

many thanks
 
Section 705 covers agricultural installs.
Using the SWA sheath as a cpc depends on it's CSA in relation to the size of the copper cores.If you do a search there are numerous threads on this,and you will find tables with SWA sizes in a simple go-no go format.
 
Also,fella,there are reasons why you need to keep livestock and earth stakes apart...search for earth rod pits,potential change,distance between beasts legs etc...loads of fun,nowt rude,honest
 
Also,fella,there are reasons you need to keep livestock and earth stakes apart...search for earth rod pits,potential change,distance between beasts legs etc...loads of fun,nowt rude,honest

Not quite sure what you're meaning is here?? A building that will be used to accommodate livestock, it is preferred that the electrical earthing system be made TT where TNC-S is the incoming supply to the farm. That's not to say that TNC-S is prohibited, it can be used where the concrete flooring of livestock housing buildings, incorporates a main bonded metal metal grid.

OP... You can extend the equipotential zone of a PME system providing you meet the requirements.
As for the armouring of SWA cables, the CSA of the steel wires will be of a sufficient size to comply as the CPC, up to 95mm. However if any main bonding is required at the load end of the submain, the SWA CPC will ''NOT'' comply and will need either an extra core in the SWA cable or a separate suitably sized earthing conductor to be run in with the SWA cable,
 
Blue = min CSA of cables SWA to comply.

(Red) = Cable does not comply.

Note: These tables relate to Complance for CPC purposes Only, and ''NOT'' for Main Bonding.

Table for 70[SUP]0[/SUP]C Thermoplastic PVC SWA cables.

Conductor CSA
Minimum CSA of SWA to meet 54G
CSA of armour 2 core
CSA of armour 3 core
CSA of armour 4 core
1.5
3.4
15
16
17
2.5
5.7
17
19
20
4
9.0
21
23
35
6
13.6
24
36
40
10
22.6
41
44
49
16
36.1
46
50
72
25
36.1
60
66
76
35
36.1
66
74
84
50
56.4
74
84
122
70
79.0
84
119
138
95
107.2
122
138
160
120
135.3
(131)
150
220
150
169.2
(144)
211
240
185
208.6
(201)
230
265
240
270.6
(225)
(260)
299
300
338.3
(250)
(289)
(333)
400
403.9
(279)
(319)
467



Table for 90[SUP]0[/SUP]C Thermosetting SWA cables operating at 70[SUP]0[/SUP]C.

Conductor CSA
Minimum CSA of SWA to meet 54G
CSA of armour 2 core
CSA of armour 3 core
CSA of armour 4 core
1.5
3.4
16
17
18
2.5
5.7
17
19
20
4
9.0
19
21
23
6
13.6
22
23
36
10
22.6
26
39
43
16
36.1
41
44
49
25
36.1
42
62
70
35
36.1
62
70
80
50
56.4
68
78
90
70
79.0
80
90
131
95
107.2
113
128
147
120
135.3
(125)
141
206
150
169.2
(138)
201
230
185
208.6
(191)
220
255
240
270.6
(215)
(250)
289
300
338.3
(235)
(269)
(319)
400
451.0
(265)
(304)
452
 

Reply to AGRICULTURAL: TN-C-S extension or TT in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
669
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

N
  • Question
In my first sparking era (late 90's) I was always told to run a neutral to the isolator, as the chances are whoever is using the machine will...
    • Like
2
Replies
21
Views
2K
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top