No disrespect, but i don't think your competent to be mucking around with a switchboard of this size going by your above proposals!! You need to maintain the switchboards fault current ratings bracing, so you would know flexible and bracing is a contradiction. You also don't cut into a switchboard and start altering or cutting into bus bars unless you know exactly what your doing of..

The 1200A ACB may also have connections to protective relays, have you checked?? That ACB IS the over current protection between the transformer and the bus bars !! As Tony has already told you ACBs of this size have a wide setting arrangement in many cases down to 60% or less. I'm also guessing that you also have little idea how to set or reset the parameters of the protection curves on an ACB

There is no need to replace this breaker anyway, as it's there to protect the bus bars and possibly the transformer, not the outgoing cable/loads, they will be protected by the distribution MCCBs or switch fuses...

Let me put it another way, an electrician shouldn't be making these sorts of dicissions on a sub-station supplied main switchboard, that is the work of a qualified Engineer...

Mark my words here, get something like this wrong, and you'll know all about it, ...but fast!!

Thanks very much Engineer 54 , i appreciate your comments and take your advice on board. However their is one point you are missing . their currently is no ACB or any protective device installed between the bus bars and the sub station only a 2000 amp main switch. other than the switch it is a direct connection between the bars and and the loop main from the substation.

With regards to the final design im happy to hand this over to an engineer to specify it correctly , but I wanted to give him or her some idea of my proposals before I did this by gauging peoples opinion on here.
but thanks again
 
Where do these 3m of tails connect to in the substation, directly to the Transformer or to a LV DNO Switchboard??
I can't believe there is absolutly no protection provided between the TX LV terminals and your unprotected main switch!!! Loops as you call it, are normally only seen at the MV/HV side of transformers, by means of RMU's (Ring Main Units)....

My advice, is to get a Qualified Electrical Engineer involved in your planned project now, tell him your requirements, and let him make the dicissions on how to go about achieving them in a cost effective way... Or, Panel manufacturers can also be given the task of providing your needs. Who will send an Electrical Engineer to assess what you have, and what you need and propose a design to meet them, based on/around their panel systems... You could ask 2 or three such manufacturers to quote on your project.
 
The MV side of the TX protection, is normally sensed from the LV side, via protection relays!! Which is why i asked if there was an DNO LV switchboard in the substation. 3m doesn't seem long enough to connect directly onto the TX LV connection bushings/bars. Could also be the location of the protection CT's, (if any) on those LV bushings. Weird set-up all round if what the OP is saying is correct...lol!!
 
only reason i asked about length of lv cables was because we did something similar lv was 12mtr with no protection ,but we were installing a c/o panel and installing new 630mm singles 22mtr run we had to install new acb cubicle near tx
 
Where do these 3m of tails connect to in the substation, directly to the Transformer or to a LV DNO Switchboard??
I can't believe there is absolutly no protection provided between the TX LV terminals and your unprotected main switch!!! Loops as you call it, are normally only seen at the MV/HV side of transformers, by means of RMU's (Ring Main Units)....

My advice, is to get a Qualified Electrical Engineer involved in your planned project now, tell him your requirements, and let him make the dicissions on how to go about achieving them in a cost effective way... Or, Panel manufacturers can also be given the task of providing your needs. Who will send an Electrical Engineer to assess what you have, and what you need and propose a design to meet them, based on/around their panel systems... You could ask 2 or three such manufacturers to quote on your project.

And ask the Engineer to do a discrimination study on the whole set up by the looks of things...
 

Reply to Air Circuit breakers in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Merry Xmas to all :D
    • Friendly
    • Like
Replies
8
Views
451
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
747
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top