Air con blowing 20a MCB a few weeks into box change in shop/commercial
T
The Ghost
Strange day, changed DB in shop couple of weeks ago from old wylex with cooked neutrals and burnt out neutral bus. Wiring was the usual sargasso sea of cables above suspended ceiling, old circuits, redundant circuits and really bad light switch arrangement. Pulled out the switch wires (six) and re-located into grids at reachable height and so on. Fully expected to be called back for RCD problems.
Got a call regards the air con MCB popping a couple of weeks in. Thought mhmm just megger cables (SWA) and flexible control cable from outside fan to unit. Not possible as could not disconnect or access cables on outside unit. I suspect the outside fan is jamming but can't even look at it as it is inaccessible. Do not really know about air con apart from the obvious general principles. Anyone up on air con? Its a Fujitsu in suspended ceiling quite old by the looks of unit.
I did say he should get a service engineer in for air con as it was not my area. I only went to see if I could identify any obvious reason for the tripping in the supply cable. So he is going to get in the guy he uses.
Checked all around the ceiling cassette in the shop no rating plate or any model info either. The MCB does not go off straight away it may do, but then it can stay on for several minutes, then only a couple of minutes very random in timing terms.
Unlikely to be a fan problem because they're usually supplied via a speed control board and fused internally.
Did you check the running current?
As per Westward, if you're not familiar with HVACR kit I'd suggest trying a C or even D curve MCB, assuming the cct can make disconnect times. If problem persists hand it over to an A/C techie.
The Ghost,
Pete999,
TrueNAS JBOD Storage Server