After educating myself with an s plan system etc, would it be a good idea to check the heating valve is sending the signal to the heat pump to say it is open and therefore turning on heating? As the valve opens (hence the heating working under hot water) but may not be telling the heat pump this.
 
Last edited by a moderator:
Hi - I think you've got a control system problem and an ASHP problem.
My best guess is the orange wire from the zone valve is not being made L so the ASHP doesn't know to make heat. If you go near those zone valves be aware there are 240V connections - Danger Morgan, Danger. Several faults can have the same effect (cabling, microswitch, motor for example). An experienced Electrician should confirm if the fault is there fairly quickly, just saying. After the control system is working properly that will still leave the defrost problem, sorry.
 
Hi - I think you've got a control system problem and an ASHP problem.
My best guess is the orange wire from the zone valve is not being made L so the ASHP doesn't know to make heat. If you go near those zone valves be aware there are 240V connections - Danger Morgan, Danger. Several faults can have the same effect (cabling, microswitch, motor for example). An experienced Electrician should confirm if the fault is there fairly quickly, just saying. After the control system is working properly that will still leave the defrost problem, sorry.

Don't worry, I may not have much experience in electrics but I know how to isolate a system and not touch live wires haha.

Frankly I don't care about the defrost issue currently as it never ices up much. As long as I get heat on demand then I'm happy
 
Hi - no no no, maybe :).
Power may not be coming into valve on the the grey wire. Or the connection from the orange to the boiler may be no more etc ...
 
Hi - no no no, maybe :).
Power may not be coming into valve on the the grey wire. Or the connection from the orange to the boiler may be no more etc ...
So the orange is the wire which tells the ASHP the valve is open and to make heat and that's what you suspect is the issue?

Are you also saying if that wire is not live then it doesn't necessarily mean the valve is faulty?
 

Reply to Air source heat pump heating issue in the Central Heating Systems area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
155
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
522
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
469

Similar threads

N
  • Article
Air Source Heat Pumps I have been thinking of going on this course but my only reservation with it is reaching out to the right clientele, has...
Replies
0
Views
134
Nwalky
N
  • Article
This is an RSS feed of thread: Heat Exchanger with AGA and heat pump Content of the thread: Hi All I have a client asking whether they can still...
Replies
0
Views
165

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top