What I would suggest if you feel able and safe - is to do a quick wire change. Before you touch any wiring you must isolate all electricity and check afterwards it is dead - do know how to do that? The easiest way to isolate is switch off the home main switch/switches which is what I recommend you do.
What we are going to check is the operation of the 2 port Motorised Valve(2PMV) for the CH circuit and check that the water pump starts.
To do this we are going to disconnect the white wire at terminal 13 at the ASHP and label with tape or a marker pen or note the number on it so its purpose is not lost. Put its end in a connector block or WAGO and then move it of harm's way.
Now, remove the wire from terminal 10 and insert it into terminal 13 and tighten up.
Re-connect power.
Set the programmer to 'Constant HW' (or advance the switch on or press override for HW).
Next we need to create a demand for HW (yes HW) by running off from the HW tank or turning up the HW set temperature. The latter is the easiest and quickest but up to you how. Now go to the water pump and observe the green lights on it. When a HW demand is created does the water pump start? If it does, go and see of the ASHP starts - it may take a little while. If the ASHP starts wait a while and feel the radiators to see of they become warm. If the pump does not start, it may be the HW demand has not been signalled so run off some hot water to much reduce the tank water temperature. Unless a demand for HW is generated the test will not begin.
Turn the HW tank stat to its lowest set temperature, when the demand for HW ends, the water pump and ASHP should shut down.
That's the end of the test. So isolate electricity and return the white wires you removed to their original terminals.
I look forward to hearing the results. We are checking the external logic ' demand 2PMV(CH) opens and when opened start water pump', and the ASHP internal logic 'if circulant water flow detected and there is an >?? Celsius temperature difference between out and return then start ASHP'
I won't give any more explanation to avoid confusing you.
Thank you, i shall try this shortly, one thing: the water pump works when I ask for HW or CH, it's just the heat pump which does not work when asked for CH only