Just carried out a pre-work survey (older property and I wanted to check it over) for a client that wants a few extra sockets and other bits and bobs. The installation has a 5-way Wylex board (I’m guessing 1980s - white/cream plastic) which has had RCD protection added externally at some point - so the entire installation us protected by the single RCD. Circuits are: water heater (no longer used for immersion), sockets (combined ring for downstairs and upstairs), lights downstairs, lights upstairs), and cooker. Earthing and bonding, Ze both fine. R1+ R2 on upstairs lighting intermittent - some roses without earths. Older imperial cable but IR tests L-N > 500, L-E > 500, N-E > 8 (suspect neutral caught or similar). If I add additional sockets, my work has to be compliant, but the single RCD plus the single ring clearly don’t comply with section 314 (division of installation)… What's the general feeling here? The client has only just purchased the property and is not cash rich... Ideally it would a new CU (plus remedial work as appropriate) but if I can remain compliant without that the client would prefer it.
Thoughts?