Hi
I completed a job recently where a hotel reception had a new desk fitted. The old desk dado was supplied via an RCD spur from the existing ring. This ring is fed from one of the very old Merlin single phase boards which I’ve been told you cannot retrofit Schneider ic60n RCBO’s in. I had to remove a couple of sockets including the existing Rcd spur from a wall backing on to a riser as the new desk needed to be flush to this wall. The existing ring was fed in pvc tube down the riser and rear entry to the sockets. Instead of using an Rcd spur to protect my alteration at this point (x4 sockets 2.5 radial in dado) is there a regs issue with instead fitting a single module plastic enclosure with a B16 RCBO - no main switch just the ring terminated straight into the RCBO? - circuit is supplied via C32 MCB. (Enclosure mounted in the riser with 2.5 LSF glanded out the bottom and penetrating the wall through to the desk dado.

Interested to hear thoughts on this.
Thanks
 
I wouldn't see any problem either, but ...
If you look in the book it says you can use BS1363 devices on an RFC - it's one of the conditions for having an RFC where the CCC of tbe cable is lower than the rating of the circuit protection.
We then get into semantic arguments. If the regs say you use BS1363 devices, does this implicitly prohibit other devices ?
 
I wouldn't see any problem either, but ...
If you look in the book it says you can use BS1363 devices on an RFC - it's one of the conditions for having an RFC where the CCC of tbe cable is lower than the rating of the circuit protection.
We then get into semantic arguments. If the regs say you use BS1363 devices, does this implicitly prohibit other devices ?
Who knows? There's this, in the OSG app H:

"Permanently connected equipment should be locally protected by a fuse complying with BS 1362 of rating not exceeding 13 A or by a circuit-breaker of rating not exceeding 16 A and should be controlled by a switch, where needed (see Appendix J)."

Based on that, I suppose the IET aren't completely against the idea of using MCBs on ring finals.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Manchester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Local RCBO protecting ring final alteration.
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
154988,
Last reply from
Pretty Mouth,
Replies
3
Views
348

Advert

TrueNAS JBOD Storage Server

Back
Top