RyanF

-
Joined
Jan 27, 2018
Messages
102
Reaction score
51
Location
Newcastle Upon Tyne
Hi everyone,

Not going to lie I am crapping my self for my AM2 exam on Monday Morning at 8:00. So I just need a few questions answered:- tell me if I am right or wrong.

I will be using a megger tester by the way.

PEFC testing 3 phase ( 3 probe test) :-

Clamp croc clip on the neutral bar.

L1-N -E
L2-N-E
L3- N -E

People say do to simply:-

L1-E
L2-E
L3-E

Keep a mental note of the highest figure.

PSCC on 3 phase ( 3 probe tesy but, put the neutral test lead/probe into the earth test probe so its now a 2 lead test)

Test between:-

L1-N
L2-N
L3-N

Mental note of highest figure.

Out of both test the highest figure is doubled as a rule of thumb as the fault current could occur between two phases. This fig is recorded on the test sheet as IPF.

For testing a RCBO on lighting circuit people say disconnect the load and carry out IR seperate, but also still test the RCBO tripping times but how would you do that? As in the exam you are not aloud to expose any live conductors during the live tests.

Also, when doing IR test you have to disconnect certain equipment. But, when doing the ring main there is outdoor socket with a neon fused spur in. How do you disconnect the neon out of the socket. Can you simply out the connections to this socket in a wago connector and put the socket back on, as there will be no conductors connected to the outdoor sockrt. But, I am still testing the conductors?

Any help would be great!

HELP!
 
To be honest not as bad as I thought. Ive got 3 hours left on my install to do the S plan and data points. All other cables/ circuits are terminated and connected. I still need to check the conductors and fixing etc against the spec.

Then on to inspection and testing / fault finding tomorow.

Would I loose marks if I use the wrong size crimps on the cpc for the swa banjo etc? Not really good with using crimps.

So are you able to stop the install midway through and carry on the next day?

Sounds like your doing good time
 
So are you able to stop the install midway through and carry on the next day?

Sounds like your doing good time

Yeah you get a total of 8 hours I believe so I cant do that over one day. So I try and get most of it done in one day then the other day is the remaining time along with the other timed units etc.
 
To be honest not as bad as I thought. Ive got 3 hours left on my install to do the S plan and data points. All other cables/ circuits are terminated and connected. I still need to check the conductors and fixing etc against the spec.

Then on to inspection and testing / fault finding tomorow.

Would I loose marks if I use the wrong size crimps on the cpc for the swa banjo etc? Not really good with using crimps.


You have loads of time left. The s plan is very simple with the diagram, just wiring by numbers.

Good luck
 
You have loads of time left. The s plan is very simple with the diagram, just wiring by numbers.

Good luck

Simon i need your help, how do you measurePEFC AND PSCC using a Megger MFT 1730 just im doing my inspection and testing soon. Like within the next 2 hours. Do you have any hints or tips for the testing, inspection and fault finding?
 
Simon i need your help, how do you measurePEFC AND PSCC using a Megger MFT 1730 just im doing my inspection and testing soon. Like within the next 2 hours. Do you have any hints or tips for the testing, inspection and fault finding?


Flat out at work again today trying to finish a substation ready for yesterday, only just seen this mate.

How did it go?
 

Reply to AM2 exam is Monday Morning Need Help with PFC testing on 3 phase and rcbo testing on lightingcircuit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
706
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
1K
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top