RyanF
-
Hello all Sparkies,
Ive got a question how would you measure Zs on the installation at the origin? Even though the install is “dead”.
How do you test the motor circuit as in IR and Zs etc? Would you test the 3 phase IR from the supply to the contactor then do the same from the load side to the motor? Same with Zs test each phase to Earth and take the highest reading from both load and supply side and add them together by doing Zs=Ze + (R1+ R2)? So test from Db to Dol. Then Dol to Motor?
Another question is how would you test Zs, Polatiry and IR of the SWA commonda socket circuit with th isolator?
Thanks everyone.
Ive got a question how would you measure Zs on the installation at the origin? Even though the install is “dead”.
How do you test the motor circuit as in IR and Zs etc? Would you test the 3 phase IR from the supply to the contactor then do the same from the load side to the motor? Same with Zs test each phase to Earth and take the highest reading from both load and supply side and add them together by doing Zs=Ze + (R1+ R2)? So test from Db to Dol. Then Dol to Motor?