Hello Guys

being a Londoner i have not had a great deal of experience with TT systems in a domestic setting.

The existing installation is in the basement, the existing earth rod is by the DB and sticking out of the ground, not inspection pit is that quite bad?
I was thinking of changing the rod and installing a pit, how long should the rod normally be to make sure i get a good reading.. on average?

all the final circuits will be 30ma RCD protected however with the DB being metal would i need to install a time delayed RCD before the DB?
 
Last edited by a moderator:
RCBOs within board will be installed

Existing Rod gives a healthy reading 0.30

Ahh mate that cover looks to be the perfect solution thanks, looks quite sturdy i guess you just bury the little stub into the ground?
 
That's an extremely good reading for a rod and would be mad to install a new rod that will probably not achieve any where near that reading.

No need for an upfront time delayed RCD, just make sure the tails are adequately supported and taken through a nylon tail gland .

You could just screw the cover to the floor and conduit down to it or clip down to it and finish it off with a stub of conduit, female adaptor and a stuffing gland.
 
Hello Guys

being a Londoner i have not had a great deal of experience with TT systems in a domestic setting.

The existing installation is in the basement, the existing earth rod is by the DB and sticking out of the ground, not inspection pit is that quite bad?
I was thinking of changing the rod and installing a pit, how long should the rod normally be to make sure i get a good reading.. on average?

all the final circuits will be 30ma RCD protected however with the DB being metal would i need to install a time delayed RCD before the DB?
 
RCBOs within board will be installed

Existing Rod gives a healthy reading 0.30

Ahh mate that cover looks to be the perfect solution thanks, looks quite sturdy i guess you just bury the little stub into the ground?

That is one heck of a low reading for a TT which I assume is in a domestic setting
Was the reading taken with the earth conductor removed from the met ?
 
That's an extremely good reading for a rod and would be mad to install a new rod that will probably not achieve any where near that reading.

Thank you lee, the sub station is one road away so that's possibly the answer, I agree and it's a very good idea to add some surface inspection port to protect it.

I read up on the RCD on the rails and I agree it would just be a waste of time passing the problem further back.
 
There is no need to install a time delayed upfront RCD if all circuits are to be provided with 30mA RCD protection.
But if fitting a dual RCD board it would be prudent to do so. Your scheme might have something to say about it as the flexible links within the board, feeding the RCDs have no earth fault protection without having the upfront time delayed RCD. This is also mentioned in the OSG.
 

Reply to AMD 3 DB on a TT system in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
282
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
780
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
792

Similar threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
785
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
947

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top