Hi all,

Currently looking for something to protect a Sub Main in a house. Supply is TT and consumer unit is to be located aprox 10m away from the incoming service. Sub main will be 25mm armoured, and all final circuits will have RCD protection.

As far as I can see, I will still need an up front 100mA RCD to provide fault protection, along with an 80A Fuse for overcurrent (and fault) protection.

Is there an all in one procuct to achieve this? If not, there is currently a plastic 4way enclosure with a suitable RCD inside, but as everything else is to be replaced/re wired, I assume this will need to br replaced for a non conbustable kind? If we replaced the enclosure with a metal one, are there suitable tail clamps for the incoming meter tails, or would a plastic gland be acceptable?
 
Hi all,

Currently looking for something to protect a Sub Main in a house. Supply is TT and consumer unit is to be located aprox 10m away from the incoming service. Sub main will be 25mm armoured, and all final circuits will have RCD protection.

As far as I can see, I will still need an up front 100mA RCD to provide fault protection, along with an 80A Fuse for overcurrent (and fault) protection.

Is there an all in one procuct to achieve this? If not, there is currently a plastic 4way enclosure with a suitable RCD inside, but as everything else is to be replaced/re wired, I assume this will need to br replaced for a non conbustable kind? If we replaced the enclosure with a metal one, are there suitable tail clamps for the incoming meter tails, or would a plastic gland be acceptable?
British General Plastic Gland Kit 2x16mm² + 1x16mm² Tails Cable | Consumer Unit Accessories | Screwfix.com - https://www.screwfix.com/p/british-general-plastic-gland-kit-2x16mm-1x16mm-tails-cable/6037p
 
Hi all,

Currently looking for something to protect a Sub Main in a house. Supply is TT and consumer unit is to be located aprox 10m away from the incoming service. Sub main will be 25mm armoured, and all final circuits will have RCD protection.

As far as I can see, I will still need an up front 100mA RCD to provide fault protection, along with an 80A Fuse for overcurrent (and fault) protection.

Is there an all in one procuct to achieve this? If not, there is currently a plastic 4way enclosure with a suitable RCD inside, but as everything else is to be replaced/re wired, I assume this will need to br replaced for a non conbustable kind? If we replaced the enclosure with a metal one, are there suitable tail clamps for the incoming meter tails, or would a plastic gland be acceptable?
British General Plastic Gland Kit 2x16mm² + 1x16mm² Tails Cable | Consumer Unit Accessories | Screwfix.com - https://www.screwfix.com/p/british-general-plastic-gland-kit-2x16mm-1x16mm-tails-cable/6037p
 
The Iet have given guidance on TT tails
They can be connected directly to a metal clad board before the Rcd as long as the tails have enhanced protection

I personally would fit a S type Rcd in a plastic enclosure fed by the tails, then on to the metal clad switch fuse
A bit junkier but a lot safer in my opinion
 

Reply to Amendment 3 and Upfront RCD/Overcurrent protection for TT Submain in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
488
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
962
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
901

Similar threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
954
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top