Hello, Could somebody explain why new regs ie non combustable dbs etc. doesn't come in until January and yet Napit have told me to use amendment 3 forms now. I designed an installation 6 months ago and so was really working to old regs, however I have been told to use new forms. As it happens I carried out work to new regs anyway apart from I fitted plastic db in cellar due to damp environment. Finally what about eicr's do I use old ones or new amendment 3 ones? Thanks for any info.
 
The amd3 regulations came into force from June this year. The only regulation that was not required to be complied with until January 2016 was the non combustible consumer unit requirement.
This was to allow the manufacturers time to accommodate this and produce enough to supply demand.

For all the rest of AMD3 you should have been using the new regulations , Zs values, cable restraints in escape route from June.

Even an installation designed before the new amendment can be, but doe not have to be, adjusted (if required) to the new requirements.
Even so I would still use the new forms to certify the installation, but class as N/A all items that are different.

For EICRs you should be already using the new forms.
 
Amendment 3, not working yet. I have asked wholesalers for months of who supplies fire rated glands for the new CU's.
Well I have found some, no thanks to wholesalers!
Electrium ( now Wylex and Crabtree) have fire rated semi blind grommets, hoorah!
See there Video, quite good.
Again they change the regs and nobody acts on it till the last moment.
There code is CRCE 1 and CRCE 2 20mm-32mm
Yes it took some finding
Rez
 
Amendment 3, not working yet. I have asked wholesalers for months of who supplies fire rated glands for the new CU's.
Well I have found some, no thanks to wholesalers!
Electrium ( now Wylex and Crabtree) have fire rated semi blind grommets, hoorah!
See there Video, quite good.
Again they change the regs and nobody acts on it till the last moment.
There code is CRCE 1 and CRCE 2 20mm-32mm
Yes it took some finding
Rez
You issue finding glands and grommets that are classed as Fire Rated are nothing to do with the manufacturers been slow on the take up but to the fact that the AMD3 does not require fire rated glanding, anyone pushing sales of such glands are just playing on the confusion of the new requirements.
 

Reply to Amendment 3 certification in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
904

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top