Amendment 3 escape routes and building control. | Page 2 | on ElectriciansForums
Discuss Amendment 3 escape routes and building control. in the UK Electrical Forum area at ElectriciansForums.net
Leesparkykent
Nearly Esteemed
Kent
So yesterday I was wiring the communal areas in a block of flats that im doing and the building control officer pops his head in with the site agent. Concrete ceilings that's having a MF suspended ceiling underneath so we are using bang in cable tie bases.......Building control officer pipes up and says not acceptable, looks in his book and quotes reg 521.11.201 at me. I say its having an MF ceiling and the new reg would only apply to wiring in or out of containment underneath the suspended ceiling. But the **** is adament and said he wants band straping screwed either side to support the wiring in the event of a fire......Prat. Anyone had similar instances with building control officers?
Straight forward really dude, make sure the window comes with a panel to supply it, if not they are easily sourced, actuators are usually 24VDC, and panel is triggered by fire alarm, ours on this current job are all via an interface on the addressable fire alarm, make sure the cable supplying the vent is of correct specification for the job, like FP200 or the like, an the panel has battery back up, I guess these will be an industry standard.
Will all depend on system required and cause/effect requirements. AOV maybe connected to fire alarm, or activate silently on its own smoke detectors. The design can be multi smoke doors per floor and/or smoke windows.....Friday you should know more.
the velux windows are simple, probablu a window actuator (12/24v) with three cores 1 = close, 2 = open, 3 = return path.
they probably have a controller somewhere for them but a 1mm 3c flex should work fine but check first.
ive seen it before where it is two core and it works by swapping the polarity over to switch between open/closed this is if it isnt spring return (close on loss of power)
He is correct about the old bangers in the corridor, if there is a fire they would melt & down the cables, we purchased the Hilti the other year for the flats great bit of kit unless all the stone has settled in the bottom of the milbank floor then it's a **** & you get to know the area's & just move it over.
corridor as the amount of cables we use tray then cable tie it then all round band every meter.
bought cracking bit of kit from hilti SDS bit with the setting tool as part of the tool for the anchor fixings no hammer any more, just drill pull top off put the anchor on the end put back up to the hole press trigger on SDS &N then start again great.
We have had this under the BS5839 for many years, and now its come into the 7671, and imo not before time. Many fire incidents have resulted in people and fireman being entangled in fallen cables and unsupported pipework. With data guys being the worst for throwing cables across ceilings. Plastic ties are possibly the worst cable support in a fire condition. Proper supported containment rawbolted into the ceiling will always be a best solution, but any metal strapping which gives hours and not minutes in a fire event is better than plastic.
Galv saddles is the answer.
Sorted...fitted it today. This one was to be activated silently on its own smoke detector.
[ElectriciansForums.net] Amendment 3 escape routes and building control.
Hes one I completed a few weeks ago...10 fire doors (2 per level) cause & effects to open fire door on activation of smoke detectors on that level only, plus activate roof vents on activation of all levels
[ElectriciansForums.net] Amendment 3 escape routes and building control.[ElectriciansForums.net] Amendment 3 escape routes and building control.
Reply to Amendment 3 escape routes and building control. in the UK Electrical Forum area at ElectriciansForums.net