Amps & generator load | on ElectriciansForums

Discuss Amps & generator load in the DIY Electrical Advice area at ElectriciansForums.net

paulmars

DIY
Joined
Sep 17, 2019
Messages
10
Reaction score
0
Location
central fl
Year 2002 two ton 240vac hvac compressor. Plaque says 21.4 amps. Paperwork says use 30a dbl breaker.

Is that 21.4 amps on each hot wire?

Air handler central hvac 120vac fan paperwork says 6.2 amps

2 fridges in house. Plaques say 6.5 & 4.5a. 120vac.

Both fridges on same hot. The 6.2 amp central fan is on the other hot.

Only other things running were modem\router and two phone charges. Smart tv & microwave were plugged in, but off.

Yes water heater was off and no one was washing or drying clothes.

Yes both fridges were cycled on during amp measurements.

6500 watt generator has a 27 amp breaker on each hot. My ammeter read 15 & 18 amps.

Should 21.4a 240vac compressor pull 21.4 on each hot? If not why does it need a 30a dbl breaker?

Can I add another fridge & window ac?

P
.
 
it may draw up to 21A when under full load.
the 30A breaker is to cover the start up current that may be considerably higher.
in theory you have a spare 9A to play with based on your measurements.

but to be fair the only way to be sure is to run it all with the loads you want on and see if everything is ok for an hour or 2.
 
So 18ax240v is 2320 watts

Slightly over 1\3 the 6500 watt capacity

I understand mtr start up pulls a lot more.
 
Year 2002 two ton 240vac hvac compressor. Plaque says 21.4 amps. Paperwork says use 30a dbl breaker.

Is that 21.4 amps on each hot wire?

Air handler central hvac 120vac fan paperwork says 6.2 amps

2 fridges in house. Plaques say 6.5 & 4.5a. 120vac.

Both fridges on same hot. The 6.2 amp central fan is on the other hot.

Only other things running were modem\router and two phone charges. Smart tv & microwave were plugged in, but off.

Yes water heater was off and no one was washing or drying clothes.

Yes both fridges were cycled on during amp measurements.

6500 watt generator has a 27 amp breaker on each hot. My ammeter read 15 & 18 amps.

Should 21.4a 240vac compressor pull 21.4 on each hot? If not why does it need a 30a dbl breaker?

Can I add another fridge & window ac?

P
.
It will pull 21.4 amps which is an actual load and the breaker is sized based on the calculated load. Which is 30 amps
 

Reply to Amps & generator load in the DIY Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
349
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
896
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I am interested in having a home generator that would provide power to my home when the power is out during hurricane season, etc. I have 2...
Replies
0
Views
689

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top