Guest viewing limit reached
dldavies
Could somebody please help me check my calculation for amps per phase for a 50KW total load over 3 phases and tell me what it should be.
Thanks in advance.
[h=3]Have you included your PF correction?
AC three phase kilowatts to amps calculation formula[/h] The current I in amps is equal to 1000 times the power P in kilowatts, divided by square root of 3 times the power factor times the voltage V in volts:
I = 1000× P / (3 × PF × V )
So amps are equal to 1000 times kilowatts divided by square root of 3 times power factor times volts.
amps = 1000×kilowatts / (3 × PF × volts)
or
A = 1000 × kW / (3 × PF × V)
[h=4]Example[/h] What is the current in amps when the power consumption is 0.33 kilowatts, the power factor is 0.8 and the voltage supply is 110 volts?
I = 1000 × 0.33kW / (3 × 0.8 × 110V) = 2.165A
You're quite correct, I hadn't included the PF figure. The new calculation I believe is 87 amps per phase.
Many thanks.
What supply voltage have you used to get that answer?
I get 90.2a, assuming its a 400v 3 phase supply
At 415V at unity PF your first answer was right.
What PF did you use for your second answer?
415v at unity gives 69.56a per phase. As Tony said, how have you arrived at 87a per phase???
I worked out the PF for the 2nd answer must be 0.75 ? ? ? ?
Amps per phase calculation
dldavies,
Afageeh,