It's the right answer but you would probably only get one mark because each of your answers are for fire protection, the same thing.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss An Awful Feeling This in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
It's the right answer but you would probably only get one mark because each of your answers are for fire protection, the same thing.
Thanks for that you have given me some food for thought there, i am going to go back and look at the previous answers you gave for the question
I would have use at the origin of the installation for exhibitions shows and stands Reg 711.410.3.4 and also temporary installations for structures, amusement devices and booths at fairgrounds Reg 740.410.3 rather than your last 2.
State the test instrument to be used to carry out a resistance measurement of an earth electrode
a) that forms part of a TT system that is protected by a 100mA RCD (1 mark)
b) used to earth a three phase transformer (1 mark)
c) used to earth a generator. (1 mark)
earth loop impedance tester for all three or earth electrode tester for all three
State the test instrument to be used to carry out a resistance measurement of an earth electrode
a) that forms part of a TT system that is protected by a 100mA RCD (1 mark)
b) used to earth a three phase transformer (1 mark)
c) used to earth a generator. (1 mark)
earth loop impedance tester for all three or earth electrode tester for all three
Earth fault loop impedance tester for a
Earth electrode tester for b and c
List three items of fixed electrical equipment that may need to be disconnected from a domestic installation before carrying out an insulation resistance test.
1. lamps,capacitors etc
2.any voltage sensitive equipment
3. any pilot lights or neon indicators
is this satisfactory
this little sh*t has been bugging me for days
List, in the correct sequence, the first three tests to be carried out on a newly installed lighting circuit.
continuity of protective conductors
insulation resistance
polarity or earth loop impedance (Zs)
i have been speaking to a couple of very experienced lads about this today and even they were not sure i would be more likely to believe its
continuity of protective conductors
insulation resistance
earth loop impedance