hi ladies and gents

I have opened a ring final circuit to add 3 sockets. All was goin well till I powered it up and it keeps tripping. I have tested and IR comes back fine. continuity also fine, all test readings are fine. the circuit has 9 sockets and has a 32 type c rcbo. any other info needed please ask.

sorry for the short message but my keyboard is dying.

thank you
 
To the op

Check the actual sockets for compression on conductors by this I'm talking about wires pinched tight against the backbox or faceplate screws , seen lots of people having this problem and funnily enough I've genuinely just come back from a callout where the customer couldn't get the Rcd to stay on and he'd added a spur himself earlier , although his jb work of art was rubbish and had to be redone he'd actually not done anything wrong there it was another single socket adjacent fixed earlier to a 16mm box flush to the wall!
Wires compressed badly with no visible nicks , I removed this cable and socket and messed about with the offending cable still couldn't see copper!

Circuit tested fully (including the tests currently being argued over, yet no one has still got the right connections even though its on the osg pics!)
 
Btw before someone starts on about diy'ers I made it clear to him how bad a job he'd done and charged him handsomely for the privilege, and got a tip!
My parting words were it would have cost you less to get someone who is qualified and competant to do it the first time round!
 
I have opened a ring final circuit to add 3 sockets. All was goin well till I powered it up and it keeps tripping. I have tested and IR comes back fine. continuity also fine, all test readings are fine. the circuit has 9 sockets and has a 32 type c rcbo. any other info needed please ask.

sorry for the short message but my keyboard is dying.

thank you

I was thinking exactly the same thing!! ......85 posts and still counting, Jesus wept!!!

The clue was in post number One! :smilielol5:
 
#87 posts of the forums "sharpest" electrical minds unable to decide between them how to sort out a RFC. Interesting reading though!

Now let me get back to working out how I get those r1, rn & r2 values on that radial socket circuit I want to install .....
 

Reply to Annoying simple circuit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
433
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Very technical :D
    • Like
Replies
9
Views
446
  • Question
It might be worth asking the customer to turn the oven on 45min before you arrive. then do an IR test on the oven from the isolator with the oven...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top