Here we go again:
"An electrical installation forms part of a 400/230V three phase four wire TN-S system with an earth fault loop impedance of 0.4Ohms.
A new TP&N distribution board fitted with BS EN 60898 type C circuit breakers has been installed for the new lighting circuits.
The new fluorescent luminaires are surface mounted.
The ground floor luminaires are controlled by a photo cell and the remaining luminaires are controlled solely by circuit breakers.
The installation is carried out in multi core steel wire armoured cables with 2.5mm copper conductors, one of the cores of the cable is used as cpc.
Describe in detail how an insulation resistance test would be carried out on one of the completed ground floor lighting circuits.
The car park is to remain operational while the testing takes place."
I understand how to do an insulation resistance test.
I would also include safe isolation procedures and warning signs
checking of leads and batteries etc.
I would disconnect the photocell and link out.
What I am not sure about is if I can disconnect the lights.
Also because the public is using the car park during the test.
Would it be better to:
1. disconnect all lights, link the disconnected cables together to ensure the circuit remains in tact and test at 500V.
2. Or test the whole circuit at 250V.
3. Or some other way.
The fact they are fluorescent lights and it may be inconvenient to disconnect them and the fact the public are at large is kind of confusing me.
Can anyone offer any assistance with this?
Cheers.
"An electrical installation forms part of a 400/230V three phase four wire TN-S system with an earth fault loop impedance of 0.4Ohms.
A new TP&N distribution board fitted with BS EN 60898 type C circuit breakers has been installed for the new lighting circuits.
The new fluorescent luminaires are surface mounted.
The ground floor luminaires are controlled by a photo cell and the remaining luminaires are controlled solely by circuit breakers.
The installation is carried out in multi core steel wire armoured cables with 2.5mm copper conductors, one of the cores of the cable is used as cpc.
Describe in detail how an insulation resistance test would be carried out on one of the completed ground floor lighting circuits.
The car park is to remain operational while the testing takes place."
I understand how to do an insulation resistance test.
I would also include safe isolation procedures and warning signs
checking of leads and batteries etc.
I would disconnect the photocell and link out.
What I am not sure about is if I can disconnect the lights.
Also because the public is using the car park during the test.
Would it be better to:
1. disconnect all lights, link the disconnected cables together to ensure the circuit remains in tact and test at 500V.
2. Or test the whole circuit at 250V.
3. Or some other way.
The fact they are fluorescent lights and it may be inconvenient to disconnect them and the fact the public are at large is kind of confusing me.
Can anyone offer any assistance with this?
Cheers.