I think if this was installed properly each individual light would be on a greg, so you can unplug all of the lights because you must remove any sensitive equipment.
You must test at 500v dc if a single phase circuit up to and including 500V.
This is a new installation not a fuseboard change and you are 100% sure of where everything is.
The SWA should be earthed so you need to disconnect any fly leads so you are just testing between the cpc and live then neutral, then neutral and live. 612.3.1 says you can connect line and neutral together, but this is not good practice and also states when appropriate (new circuit).
The linking out of the photocell is a must as this is sensitive equipment, and you would not test the switch live if not linked to the feed.
**You must notify the owner of the property that you are about to do an insulation resistance test**.
This is a classic 2391 question because you have to understand how to use SWA and install it to be able to answer it.
You must test at 500v dc if a single phase circuit up to and including 500V.
This is a new installation not a fuseboard change and you are 100% sure of where everything is.
The SWA should be earthed so you need to disconnect any fly leads so you are just testing between the cpc and live then neutral, then neutral and live. 612.3.1 says you can connect line and neutral together, but this is not good practice and also states when appropriate (new circuit).
The linking out of the photocell is a must as this is sensitive equipment, and you would not test the switch live if not linked to the feed.
**You must notify the owner of the property that you are about to do an insulation resistance test**.
This is a classic 2391 question because you have to understand how to use SWA and install it to be able to answer it.