State the;
i) tests for insulation resistance to be undertaken on a 230v circuit contaning surge protection devices which cannot be disconnected. -I am i being dumb here? Phase-Neutral and Phase-Earth

ii)The test Voltage- 250V

Thanks
 
Test across L-E, N-E and L-N, or L+N-E @ 250V, as the SPD is connected across L-N, L-E and N-E

Min resistance at least 1Meg Reg. 612.3 (BGB)
 
Last edited:
Just be careful to refer to 'E' as the Circuit Protective Conductor, 'L' as the Line conductor not phase conductor, and remember that Neutral is a 'live' conductor......City & Guilds will have you in anyway they can!
 
State the;
i) tests for insulation resistance to be undertaken on a 230v circuit contaning surge protection devices which cannot be disconnected. -I am i being dumb here? Phase-Neutral and Phase-Earth

ii)The test Voltage- 250V

Thanks

If it can not be removed then connect L and N together and test to earth @250v, note it on the test sheet as limitation.
 
If it can not be removed then connect L and N together and test to earth @250v

It is for the 2391, they may, depending on the centre, want the full test sequence.

You can never tell with C&G
 
Last edited:

Reply to Another 2391 question! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
309
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
832
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
930

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
  • Question
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...
2
Replies
24
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top