Spin, in reverse order- TT.
Did I say there was a REG number that said there was, no. Don't wiggle out of being corrected by playing with my words. Read exactly what I said. That said, I think 411.5.2 note 1. covers it. Even so, I am fairly certain that the 'essence' (look that up in legal definitions) of the IEE/IET/EAWR publications cleary say that a TT should have an RCD, and especially where the disconnection times cannot be met by normal means. YES they also allow for deviation, and exception, which is what you are getting at, but I can see you standing in the dock argueing why you went against everything and did not fit an RCD where the disconnection times could not be met. That would work.
I need a beer. Back in 5.
Why advise people of loop holes? Is it not better to go down the better safe than sorry route?
I'm sorry, but your posts in this thread have been rather pointless.
This thread is in relation to a question from the 2391 exam.
An exam that as I understand it, requires the examinee, to show a thorough understanding of BS7671 and the requirements therein.
I am also reliably informed, that the examiners for the 2391 are very hot on use of correct terminology and units of measurement.
It's not about loop holes, or wiggleing when being corrected (particuarly as I haven't been corrected in this thread).
It's about reading the question, determining what is being asked, and answering the actual question, not what you think is the question.
I will once again, point out that the question refers to a circuit, and that in BS7671, the only place where there are requirements for RCD protection for a circuit, is in Chapter 7 (Special Locations).
In the general part of the BS7671 Chapters 1 to 6, there are requirements for additional protection for socket-outlets, mobile equipment used outdoors, and for cables concealed in walls, that are not provided with another acceptable method of additional protection.
There is no requirement in BS7671 for RCD protection in a TT installation, it is the preferred method.
When an RCD is used as fault protection in a TT system, the RCD is not then considered as additional protection.
The question from the 2391 exam paper, asks for one condition, where additional protection is required.
Therefore it is not neccessarily a TT system.
The question indicates that the installation is an office, as such the requirements that apply to ordinary persons are not applicable.
The question refers to a circuit, so the requirements of BS7671 that apply to anything that is not a circuit are, not applicable.