MarcT
The trouble with TN-C-S systems is that although they provide a good Ze reading, their integrity is not guaranteed by the DNO. As far as i'm aware, the issue with the TT outbuildings started when a guy got electrocuted when his swimming pool metalwork (which was connected to a TN-C-S earth) was a different potential to the earth outside. We are therefore advised (by tutors at least) not to bring TN-C-S outside, and to earth a covered metal sheath to the MET, and an exposed metal sheath to the rod in the outbuilding. In this case there is extraneous metalwork common to both buildings. I think Des's solution is correct in this case. Its hard to find regs to corroborate your beliefs as well. However when I get stuck, I look for regs in a different situation but the same problem. For instance, caravan parks don't export TN-C-S for the same reason, but on the other hand if the the metalwork in the garden happened to be to do with a swimming pool instead of service pipes, then it is advised to bond them to an electrode as well as the TN-C-S
There is a small note on page 171.
The thing to remember with TN-C-S is that it's 0v nearly all of the time
There is a small note on page 171.
The thing to remember with TN-C-S is that it's 0v nearly all of the time