Hi folks,
story is, TNS supply to one side of a semi detached property. A three phase head, one for the property I'm working in, one for the adjacent semi and one unused.
The supply for the adjacent semi runs in VIR singles in conduit from the main head. Whils working away on my job, the neighbour pops in and asks me if I can have a look at his installation as he has been suffering from the single RCD covering the board tripping over the last month or so.
So, late yesterday afternoon had a look. First thing is Ze is 514 ohms. The board is tucked away under a stair and really difficult to access. I wasn't able to see how the main earthing has been achieved, but I'm guessing it's via an old lead water main.
Now, the question. Is it acceptable/permissable to run a 16mm earth from the suppliers head (where the property with the high Ze takes its supply from) next door? If not, it's going to have to be PME if available or TT. There is something that strikes me as not quite right taking the earth from the main head in the neighbouring property but that might just be me - it would certainly be the easiest option.
Still have not had time to investigate the cause of the tripping.
Opinions/advice welcome!
Regards.
story is, TNS supply to one side of a semi detached property. A three phase head, one for the property I'm working in, one for the adjacent semi and one unused.
The supply for the adjacent semi runs in VIR singles in conduit from the main head. Whils working away on my job, the neighbour pops in and asks me if I can have a look at his installation as he has been suffering from the single RCD covering the board tripping over the last month or so.
So, late yesterday afternoon had a look. First thing is Ze is 514 ohms. The board is tucked away under a stair and really difficult to access. I wasn't able to see how the main earthing has been achieved, but I'm guessing it's via an old lead water main.
Now, the question. Is it acceptable/permissable to run a 16mm earth from the suppliers head (where the property with the high Ze takes its supply from) next door? If not, it's going to have to be PME if available or TT. There is something that strikes me as not quite right taking the earth from the main head in the neighbouring property but that might just be me - it would certainly be the easiest option.
Still have not had time to investigate the cause of the tripping.
Opinions/advice welcome!
Regards.