A couple of months back one of my neighbours let me know that they were having a new kitchen fitted in their rental property. The complete works were to be undertaken by a very well known major DIY chain. They apologised for not getting me involved (which was very nice of them) but the DIY chain "have their own people".

So here we are 5 weeks after the works are complete. In the kitchen the electrics required modification to incorporate some new sockets.

My neighbour has been chasing said DIY chain for the certificate and Part P notification and nothing has been forthcoming. An exchange of email has taken place and the outcome, so far, is that the kitchen installer did all the work on the kitchen, including the electrics, but he's not registered, nor could he test, nor could he notify. The fitter is not an employee of the DIY chain

So they've asked me to get involved!!!!!!!!

I'm going to speak to the installer tomorrow to get his side of the story.

I've taken a quick look at the new kitchen and the "old style" cooker point has been covered over and I'm guessing that the new sockets were run as a radial off this point. The "old point" is completely hidden by a wall cupboard so its anyones guess how the "extension" to the cable was made.

My thoughts are:

Who can now notify this? (I'm happy to do an EICR on the specific changed circuits)
What tactic should my neighbour take with the DIY chain?
Who's responsibility is it to talk to LABC? The DIY chain, the installer, my neighbour?

My thinks this is going to be protracted as my neighbour knows about Part P etc PLUS his letting agent is asking for the certificates!
 
Last edited by a moderator:
UPDATE.

My neighbour finally got the (NICEIC) certificates and we went in to have a look before the new tennents move in.

Circuit 1 modification

MWC confirming 2G & 1G sockets added to what was the cooker circuit, no comment about changing the MCB to the new 32A RCBO, nor the 2.5mm cable added to the "end" of the old 7/029 cable.

Me thinks the MWC should state that the MCB has been changed to the RCBO
Why has he fitted a 32A breaker to a radial where the last 3-4 meters are 2.5mm cable?
No comment about the JB concealed behind new cupboard
(No comment on the fact that the kitchen fitter did all the install work.)

Circuit 2

Spur off existing 2G socket

RCD test times for 1x and 5x almost identical - which looks unusual.


Neighbour not happy and about to pen a letter to the big shed who they ordered the new kitchen off
 
I would remind the neighbour that you weren't involved from the start and wish to stay that way! But I would then ring the kitchen company and advise them from this point on they should use a qualified electrician (You), and not this other muppet.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Another fine mess??????
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
42
Unsolved
--

Advert

Thread statistics

Created
Octopus,
Last reply from
drew35,
Replies
42
Views
4,268

Advert

Back
Top