We've had to replace the single oven and discovered that both single oven and hob were hooked into the same terminal strip which was massively overloaded. We've now installed an induction hob with is plugged in to a plug socket on the isolator switch for the oven. The problem we have now is that the cable coming from the isolator switch isn't long enough to reach the oven anymore and we can't replace the cable without ripping out plaster board and tiles. I'd like to extend the cable using a junction box and a 1 metre length of cable.

It's a 32A fuse on the CU and the oven is rated at 2.5kw/h so using the regs and diversity factor it works out at 11A + 5A (plus change, 16.4A really) for the socket on the isolator. The cable coming from the isolator appears to be 4mm stranded flex cable rather than the 7 solid core cable.

My question is, can I just attach a junction box onto the cable and run another cable to the oven. Do I need to find another 4mm cable or would 6mm do it? Does it need to be stranded or can I used solid core?

Hopefully that all makes sense.
 
Been trying that, for various work reasons and other family commitments we can't be around for an electrician to visit during the day. We've been let down twice by electricians not turning up, hence why I'm doing it myself.
 
what he said ^^^^^^.call in a local SPARKS. a couple of members are in your area. for the sake of a few quid, you'll get good advice and have the installation done safely.
 
Been trying that, for various work reasons and other family commitments we can't be around for an electrician to visit during the day. We've been let down twice by electricians not turning up, hence why I'm doing it myself.
obviously you've not contacted a reputable electrician. if i promise to turn up , i do so. any problems with making an appointment, i phone or text to rearrange. there's no excuse for not turning up. your time is as valuable as mine is, so a decent sparks will appreciate that. we're not gods, even if some of us think we are. ( sound like a plumber now. but plumbers being plumbers can't spell they think they are gods, but spelt right it's dogs).).
 
Hi,i feel you may struggle to get anybody to commit,to a method of extending a circuit,on an unknown installation.

The calculations you described,have very little to do with the choice of materials and method,in altering whatever you have.

What type of test equipment have you used to check the existing circuit,and will use to check any addition?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Nottingham

Thread Information

Title
Another oven thread (hopefully with a difference)
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
7
Unsolved
--

Advert

Thread statistics

Created
ChelseaNick,
Last reply from
Deleted member 105166,
Replies
7
Views
1,053

Advert

Back
Top