Basically just want anyone to pick me up on anything I may have missed or planned completely wrong!

4mm2 from 32a mcb with RCD protection run from c/u to exterior, down exterior wall in conduit and under ground in cable pipe for about 10m then terminate into garage c/u.

Distributed to a 20a and 6a fuse for an A3 Radial and Lighting circuit.
 
No. T&E, the cable pipe is specifically made for this I'm told. ¬.¬
20mm Black metal conduit.
And yes I will be using the RCD on the Main CU and a DP isolator on the Garage CU

Thanks for the help.
 
Last edited by a moderator:
Yeah I guessed that would be the case but as there's no spare ways on the non rcd side of the house CU it would be a ball ache to re-arrange.

(bearing in mind this is a favour so don't want to spend too much time there)
 
Yeah, I would have done that personally, but the 'favouree' ( my brother) already has the materials and doesn't want to spend more money so I'm kinda limited!
 
Cheers mate. Just one of those situations where someone gives you un-ideal materials and situations and you start questioning what's kosher. aha.
 
Would it be possible to cut down the Busbar on the RCD side, jog over the MCBs and put a longer piece of Busbar on the NON-RCD side?
I guess at the end of the day, it's between you and your Brother to decide what's more inconvenient.
The possibillity of a fault which would cause the RCD to trip, or the hassle involved with providing the RCD protection at the garage RCD.
 
Last edited by a moderator:
I'd much rather have separate rcd/rcbo protection in the garage CU. If the trip goes it'll take out the lights and power in the garage which is a potential safety concern.
 
No. T&E, the cable pipe is specifically made for this I'm told. ¬.¬
20mm Black metal conduit.
And yes I will be using the RCD on the Main CU and a DP isolator on the Garage CU

Thanks for the help.

One thing that no-one has mentioned here yet, ....is the use of 20mm black metal conduit in a direct buried situation!! Not a very good idea at all, it could be totally corroded, or in serious need of replacement within 5 years. It is not and never has been specifically made to be used as a buried duct, that's just pure Rubbish i'm afraid!! It is only good for dry interior installations, so not even good for surface mounted exterior work!!!

Never use anything made of ferrous metal when being buried in the ground. Heavy (thick walled) PVC pipe is always going to be your best option, when being used as a protective cable duct...

So ''Don't'' use it, your brother will soon be regretting it, ...big time!!!
 

Reply to Another power to garage post... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
692
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
605

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top