Fitted a standalone fused 30mA RCD unit today protecting a spur from existing circuit wired directly from MCB in CU. RCD FCU is mounted adjacent to CU. CU has 100mA RCD upfront (Crabtree) & is populated by 60898 MCBs. 30mA RCD x1 test was fine (28ms) but the x5 test trips 100mA as well as 30mA RCD with a result of 41.80ms. Test is carried out from new socket outlet. Furthermore, if the 100mA RCD trips, upon resetting it the 30mA RCD trips of it's own accord.
Anyone have any ideas as to what might be occuring? Cheers
 
Is this a domestic property?
if it is why have you got a 100mA RCD - change this to a 30mA and forget the 2nd RCD - the 1st will protect it.

Easier and cheaper for you and the customer.
 
Is this a domestic property?
if it is why have you got a 100mA RCD - change this to a 30mA and forget the 2nd RCD - the 1st will protect it.

Easier and cheaper for you and the customer.

It is a domestic property, 100mA RCD already in situ, one of the older style RCDs (big chunky thing that takes up about a third of the board). Felt it would easier to fit standalone RCD protecting part of install I'm concerned with rather than trying to source an old 30mA Crabtree chunky which would ultimately effect entire install.
 
What dont you change the whole board?
You can get fully loaded ones for less than ÂŁ70 now - MK as well if that's the quality you want (Yes I have seen the posts about MK boards)

I have found that fully loaded CUs are now cheaper than some RCDs.
 
What dont you change the whole board?
You can get fully loaded ones for less than ÂŁ70 now - MK as well if that's the quality you want (Yes I have seen the posts about MK boards)

I have found that fully loaded CUs are now cheaper than some RCDs.

If it was my own property then I probably would but it's not. At the end of the day the customer wanted an additional socket in their hallway which I provided within the regs, all tested etc and at about a quarter of the cost to fit & test a new CU.
 
Remove the 100mA RCD and test it that way - then re-install the 100mA RCD.

You cant guess at that, the EIC requires exact readings, if you guess at it, its not worth the paper its written on, and your neck is on the line if the RCD is faulty
 
they do only trip on the load side, but you can have extra current flow in the neutral return and that will trip it.
The RCD is looking for a difference of (100mA for a 100mA RCD or 30mA for a 30mA RCD), the difference can be on the line or the
neutral, but if there is a difference then it will disconnect the supply.
 

Reply to Another RCD problem in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
774

Similar threads

In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
677
davesparks
D
I fitted a Mem MR30 Pod and MCB, about ÂŁ75 for both.
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top