Another RCD problem | Page 2 | on ElectriciansForums

Discuss Another RCD problem in the UK Electrical Forum area at ElectriciansForums.net

jibjob

-
Arms
Joined
Mar 13, 2009
Messages
133
Reaction score
17
Location
Cheltenham
Fitted a standalone fused 30mA RCD unit today protecting a spur from existing circuit wired directly from MCB in CU. RCD FCU is mounted adjacent to CU. CU has 100mA RCD upfront (Crabtree) & is populated by 60898 MCBs. 30mA RCD x1 test was fine (28ms) but the x5 test trips 100mA as well as 30mA RCD with a result of 41.80ms. Test is carried out from new socket outlet. Furthermore, if the 100mA RCD trips, upon resetting it the 30mA RCD trips of it's own accord.
Anyone have any ideas as to what might be occuring? Cheers
 
I'll try it out just to see out of curiosity, but I would've thought unless there was a fault on the load side of the RCD then it wouldn't trip. If it's not supplying anything (no load) the RCD still has 230v on one side and 0v on the other yet it doesn't trip, when there's an inbalance under load it will trip. I still can't see really how the supply could trip it.
I am a bit tired mind you and could be having a senior moment !!!!!!!!!
 
Im thinking as the jibjob said the supply was knocking the RCD out, but when the MCB is turned off, cutting the power (also the isolator is off) - there must be a earth leakage between the CU and the isolator on the line side.

If this was on the neutral side the RCD will still be tripping out.

The other problem might be an issue with the cpc on the cooker circuit - do a Zs on that as well and a R1 + R2.

What supply do you have? TNC-S??
 

Reply to Another RCD problem in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
774

Similar threads

In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
677
davesparks
D
I fitted a Mem MR30 Pod and MCB, about ÂŁ75 for both.
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top