FatAlan

-
Trainee
Nearly Esteemed
Supporter
Joined
Sep 16, 2016
Messages
2,065
Reaction score
1,993
Location
Surrey
Ok, so there have been a number of threads on old lighting circuits with no CPC. Also noted that it’s a no no to borrow a route to earth from another circuit.
In this scenario I have two lights atop of brick gate pillars. I have good continuity and sound IR between the two pillars along with a CPC. However there is an armoured feed from the house which comes up under one of the pillars. The end of the amour is not accessible due to concrete and block paving. I have live and neutral conductors but no earth. Would it be acceptable to run a new separate earth conductor back to the origin of the SWA also confirming that the SWA is correctly earthed at the origin?
 
Ok, so there have been a number of threads on old lighting circuits with no CPC. Also noted that it’s a no no to borrow a route to earth from another circuit.
In this scenario I have two lights atop of brick gate pillars. I have good continuity and sound IR between the two pillars along with a CPC. However there is an armoured feed from the house which comes up under one of the pillars. The end of the amour is not accessible due to concrete and block paving. I have live and neutral conductors but no earth. Would it be acceptable to run a new separate earth conductor back to the origin of the SWA also confirming that the SWA is correctly earthed at the origin?

Is the armour earthed at the supply end?
 
Ok, so there have been a number of threads on old lighting circuits with no CPC. Also noted that it’s a no no to borrow a route to earth from another circuit.
In this scenario I have two lights atop of brick gate pillars. I have good continuity and sound IR between the two pillars along with a CPC. However there is an armoured feed from the house which comes up under one of the pillars. The end of the amour is not accessible due to concrete and block paving. I have live and neutral conductors but no earth. Would it be acceptable to run a new separate earth conductor back to the origin of the SWA also confirming that the SWA is correctly earthed at the origin?
I'm not sure it is a no no to pinch an earth from another circuit.

See reg 543.1.2
 
Just thought it would be bad practice to rely on a route back to earth via another circuit which without copious amounts of labelling, could be decommissioned leaving the other circuit unprotected.
 
I must admit this could be an issue as a cpc covering more than one circuit probably harks back to the day where containment such as conduit was used as the shared cpc, frowned upon now but still perfectly acceptable. I think you need to take a view as to whether this is likely to happen but as it stands you would be doing nothing outside of the Regulations.
[automerge]1568230856[/automerge]
Do you intend just to run a cpc back to the source of the cable, if so how would this involve a borrowed cpc.
 
Last edited:
I must admit this could be an issue as a cpc covering more than one circuit probably harks back to the day where containment such as conduit was used as the shared cpc, frowned upon now but still perfectly acceptable. I think you need to take a view as to whether this is likely to happen but as it stands you would be doing nothing outside of the Regulations.
[automerge]1568230856[/automerge]
Do you intend just to run a cpc back to the source of the cable, if so how would this involve a borrowed cpc.
I can get an easier route back to another circuit (outside socket) if not an option I can find another route for a conductor back to the source but it would involve digging up a small section of concrete.
 
I would apply professional judgement to using the same cpc for multiple circuits. Is it obvious that the cpc is common to multiple circuits and how much risk is there of someone disconnecting it?

I regularly run multicore SWA to carry multiple circuits in stage lighting installations, the armour is the cpc for multiple circuits which is obvious to anyone looking and not easy to disconnect without disconnecting every circuit.

However a cpc taken from an outside socket to a gatepost to connect to the lights is not obvious and very easy to be disconnected.

How would the new cpc back to the origin of the SWA be installed? Would you be burying it?
Can you trace and expose the SWA at any point in its run? If so you could cut and joint it at that point and extend it to the gatepost to do the job properly.

The problem with running the seperate cpc is that you still leave a mystery SWA to T&E transition joint under the ground.
 
I would apply professional judgement to using the same cpc for multiple circuits. Is it obvious that the cpc is common to multiple circuits and how much risk is there of someone disconnecting it?

I regularly run multicore SWA to carry multiple circuits in stage lighting installations, the armour is the cpc for multiple circuits which is obvious to anyone looking and not easy to disconnect without disconnecting every circuit.

However a cpc taken from an outside socket to a gatepost to connect to the lights is not obvious and very easy to be disconnected.

How would the new cpc back to the origin of the SWA be installed? Would you be burying it?
Can you trace and expose the SWA at any point in its run? If so you could cut and joint it at that point and extend it to the gatepost to do the job properly.

The problem with running the seperate cpc is that you still leave a mystery SWA to T&E transition joint under the ground.
My chain of thought Dave. Ideally I’d like to find the SWA feed closer to the gate post, cut, joint and re feed back into the base but I suspect it enters under the block paving. May be some digging at the flowerbed at the house end wool give a better idea of the route.
 
Modern wiring systems understandably consider a cpc unique to one circuit with the days of containment acting as an overall cpc long gone. I would and have ditched a redundant cable from a board without ever considering whether connected cpc was still serving a purpose so you are correct in considering whether this option is viable.
 
After wasting an hour or so digging for the SWA this morning I came up with the obvious solution. Just fuse down from the outside socket radial that I was going to borrow the earth from and try out one of them there Quinetic remote switches. I take it that the remote switch units will still operate from within a weather proof box?
 

Reply to Another..Replacing lost CPC? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
783
  • Question
There is no homework, and I'll never see these photo again.
Replies
3
Views
620

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top