As above the chest level from ground ,metal ANPR housing has no connection to earth ,it has monitors modems and a camera inside with a 230 volt supply run from out totem pole lighting . Its on a 6 amp rcbo.
the ZS measures 1.93 ohms
cpc to metal case measures 158 ohms so its an extraneous conductive part.

while im here to conduct an EICR we are not permitted to present an unsatisfactory eicr so its most likely down to me to make it satisfactory.
 
I think most people might suggest sabotaging said ANPR camera....

Not me, of course. Law abiding citizen and I certainly don't drive around in a van with an expired MOT.......
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

newfutile

Arms
Supporter
-
Joined
Location
hemel hempstead
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
ANPR metal housing not connected to electrical earth
Prefix
N/A
Forum
Lighting Forum
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
newfutile,
Last reply from
newfutile,
Replies
2
Views
928

Advert

Back
Top