Hmm.. yes, one does wonder on the level of risk they claim.bad for technical reasons, or bad for their profits?
If the RCBO disconnects because of a neutral earth fault then obviously that fault has not been cleared and remains in place (albeit the power is disconnected from the fault). This is clearly not a good situation but in practice this will not be an issue with your setup. The problems will occur if you have discriminating protective devices in series. e.g. 100mA time delay RCD as main switch and 30mA RCBO for the circuitThanks for the comments. I suspect the original estimator just didn't think I'd go for the more expensive solution, so didn't do more that mention it in passing. We have 11 circuits in the house, so it sounds like it might have added £300 (Hager board). Knowing what I know now I would have gone for that. On the other hand in four years the only trips have been two resulting from a faulty dishwasher. So maybe the advantage is more theoretical than real.
So on the technical side I was trying to think whether leaving the N still connected on the fault circuit could ever be an issue, but I don't see anyone saying that.
Tony S
On a fault the first protective device operates, as it should, however as it has not cleared the fault the next protective device upstream also operates and can cause unrelated circuits to power down and cause nuisance.