We had one of our guys on site checking a 10 or so year old system today (not ours). It is set up as two single phase SMA inverters, on two separate phases of a three phase supply. Both inverters have the following error "VAC BER Disturbance" which is a high grid voltage error.

When testing the grid voltage with the AC isolators turned off, the reading was 220 volts per phase, when turned on, this went to 400v. Obviously the inverters weren't generating. He then disconnected the inverter completely from the isolator, turned it on again and the grid voltage stayed at 220.

We have spoken to SMA about this and they say it can't be the inverters as quote "they don't produce voltage" but we can't see how it can be related to anything other than the inverters given that that the issue only occurs when the inverters are physically connected (even though they are not generating).

Any thoughts?

I am not an electrician, so if I've missed something obvious, don't shout!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Any ideas?
Prefix
N/A
Forum
Solar PV Forum | Solar Panels Forum
Start date
Last reply date
Replies
2

Thread Tags

Tags Tags
ideas

Advert

Thread statistics

Created
CBR600,
Last reply from
Energetic,
Replies
2
Views
1,139

Advert

Back
Top