Been working on a 1970's flat this week and it's wired in this stuff : Singles and 'sort of' old style plastic semi flexible conduit. The thing is the ring looks like they've only wired the cpc in 1mm !!

[ElectriciansForums.net] Anyone come across this before....?

(Whoops I've posted this in the wrong forum - please could one of the moderators move to 'general electrical forum' for me please)
 
Last edited:
Quite possibly only 1mm, you'll just have to take it into account for expected results when testing the circuit. It looks like solid core singles as well.
 
Yes it is 1mm earth, recently rewired a number of these properties, speaking to one of the older blokes at work these were wired mid 70s. The outer sheathing was alledgedly used to enable the property to be rewired without causing any damage - not that i would like to try
 
Funny you posting those pics I've been working with the same stuff last couple of weeks.
 

Attachments

  • [ElectriciansForums.net] Anyone come across this before....?
    ImageUploadedByTapatalk1318976123.840844.jpg
    24.5 KB · Views: 38
  • [ElectriciansForums.net] Anyone come across this before....?
    ImageUploadedByTapatalk1318976144.554153.jpg
    29.1 KB · Views: 39
  • [ElectriciansForums.net] Anyone come across this before....?
    ImageUploadedByTapatalk1318976164.011875.jpg
    33.1 KB · Views: 39

Reply to Anyone come across this before....? in the Business Related area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
813
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

Your biggest mistake is admitting to a mistake.... If theres no witnesses, it didn't happen. However.... A few golden rules.... Never trust...
Replies
6
Views
67
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top