Anyone know about SNE? | Page 3 | on ElectriciansForums

Discuss Anyone know about SNE? in the Australia area at ElectriciansForums.net

Rockingit

-
Mentor
Arms
Supporter
V.Nearly Esteemed
Joined
May 25, 2011
Messages
6,670
Reaction score
7,047
Location
Somerset
Got a new supply on a site, DNO delivered it as an SNE (so that's TN-S, yes?), 80A fuse in a 100A labelled head (yes, very clever).

But, I was there when they did it and they only ran a 'single' concentric 16mm in straight from the pole, so I can't see where the N/E separation is at all. Got a Ze of .67 so it's behaving like a TN-S.

But also, as I understand it, the DNO's aren't supposed to provide end dwellings with TN-S straight off the pole?

I'm going to be getting in a bit of a bun fight with them (DNO) over something else soon, so I'd like to be as overall gen'd up as possible!

Cheers.
 
Sorry E54 I was being a bit harsh on the DNO’s, I was commenting on the chances of them tidying up the their installation on the pole.

That transformer has me puzzled, the LV is classic for three phase 4 wire. I have seen some transformers where a standard tank is used and blanks fitted to unused bushings.
 
Right chaps, back from the brink......was talking to a Western Power design/engineer/planner on the phone earlier who had the lines up on her screen.....seems the guys who attended site either didn't know their arses from elbows (and, you know what? I REALLY hope it wasn't that!!) or just spun me some line because they couldn't be bothered. So: as far as WP are concerned, the overhead HV side is 3 wire 3ph and the LV output is separate L, N, E. Hence why it's been presented as TN-S at the intake.

On another note, it's not looking good for the connection of a ground source heat pump off that line!! :(
 
Yes, it's not definite yet, but she advised me 'not to do much more' at the moment!! I'm NOT looking forward to that particular conversation with the client........

I think the concern is more about harmonic disruption back on to the overhead network rather than a loading one. The specified Flicker standard on that particular pump is the worst one, apparently. Don't know much about flicker so will take her word for it!
 
Last edited:
And the latest development is.......

WP have just realised that it's only a 15kW transformer. The harmonics they can deal with, even all the other motors and pumps I'd overlooked telling them about isn't going to phase them. But shear numbers of amps will!

The planning engineer and I have finally agreed a figure of 98A as a 'working load' (given that the after-diversity calcs are about 150A).

Cost to upgrade the pole transformer: ÂŁ4.5k and the client will have to move to whole-current metering which is also likely to smart a bit! Lead time is 6-8 weeks. Client wants to move-in in four.........
 
I've still got a call booked for a planner to attend site anyway due to loading issues (AFTER diversity, and even with a pinch of fairy-dust hope and fingers crossed my calcs are running at 140A, almost half of which are on continuous duty - on an 80A head [mis-labelled as 100A]).
I can't see you getting a 100A supply, with a Ze of 0.67Ω.
In fact I'm suprised they allowed 80A, you sure it's not 60A?
 
spin - its all irrelevant now, but I know for certain its an 80A 1361 as I took the carrier apart! And no, the DNO don't want to come and arrest me!!!!
 

Reply to Anyone know about SNE? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top