Came across this board today while looking for a fault on the supply to electric gates. The house is only 2 years old. It was wired by an NICEIC domestic installer. The 32amp MCB's are for ring mains circuits.
1 - is that 2.5 into the last 32A? - nice
2 - lot of rings and load on the RCCD. hope the diversity calcs have been checked. may just be for convenience but still are they really needed to be 32A then?
3 - better to put larger breakers closer to the origin ie make the 16A the furthest from the RCCD.
Not only is it 100mA but it is S type. This was a split load board. All sockets were on this side. The other side with lights and cooker ect had another S type 100mA. The whole place was a joke. The incoming suply is TT and at the main meter the guy has an 100 amp main switch, come out of it are 2 16mm split cons. 1 goes to the garage which is a run of about 5 meters. In the garage board there is no RCD protection at all. The other split goes on a run about 25 meters to the house. In the house I had a quick look at a few things. Downlights in the kitchen and bathroom have no joint boxes just choc block connectors. The list goes on.
overzealous type S usage and completelly forgot the 30mA requirement seems to be the case. Must be too late seeing as I commented on the 80A but ignored to comment on the more obvious type S and 100mA, cant see the wood for the trees syndrome or just late. good one. customer probably couldnt see a problem with anything on your list just to anoy you saying "but it is new" or something like that.