S

sparkyman65

I have been asked to connect some Apollo heads and bases which I have no issues with but I have an idea the the sounder base and the head can't be consequential number ie base 1 head 2

Is this the case or do all the bases have to be addressed and then the heads

It's Apollo xp95 kit catechism panel and only 2 loops with no separate sounders

Thanks in advance for any replies
 
tazz is your man for this, mate.
 
All separate addresses mate or the panel will scream double address all night been to a few nice new panels all double addresses not a nice job sorting it out
 
Yes I knew they had to be different addresses just just seem to recall that u would have to address sounder bases say 1-10 and the heads from 11-20 not base 1 head 2 base 3 head 4 and so on ..
 
I have just remembered I think it was something quirky with the dip switch on the Apollo bases 1 was actually 0 and vice versa
 
You have 126 address in total and as long as every device, including sounders have a different address all will be ok There is no order they have to be in, so base sounder 001 and smoke detector 002 or all sounder bases 001-020 and detectors 021-040 any combination is fine. As stated above what out for older sounder bases, some of the dip switches are incorrect and arse about face. If you can get your hands on a Apollo loop tester, this will save alot of time trying to sort out double address. If you run out of addresses, or you wish to be lazy, leave base sounder addressess at 001 and autolearn panel, this will put all base sounders in Hi address, 127-245, the tick base sounder fitted in software.
 
Last edited by a moderator:
Xpert card goes into base to address the detector, the dip switches on the base are to address sounder, as stated what out for the old bases have reverse switches
 
No aslong as they are all different, than thats ok , so you can address all call points 001-020 and all smokes 021-050 no matter where they are on the loop. Some guys address them this way so they know how they have been fitted, My best advice is to mark the addresses on the drawings for reference later.
 

Reply to the thread, titled "Apollo fire alarm" which is posted in Security Alarms, Door Entry and CCTV (Public) on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top